Power Distribution and Digital Support
Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-11-03 03:12 AM
Hi,
I am replacing a dataconsentrator that is not a live anymore.
How do I reset exsisting powertags for connecting to a new PAS800L? They will not show in EPC.
They are blinking red light every second bcause they have lost commuication with the old dataconsetrator.
BR
GIA
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-03-04 12:36 AM
Unpower and then power on.
https://community.se.com/t5/Gateways-and-Energy-Servers/replace-powertaglink-to-a-Panel-server/m-p/4...
I just have PowerTag Flex and it blink all time red even I take power off and then on. It won't go pairing mode.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-03-07 11:55 PM . Last Modified: 2024-10-15 02:47 AM
If device is not powered and you put power on. It will blink red slowly. You can't reconnect it to new server right a way. Device need to be powered until it start blink red rapidly and then reboot it to pairing mode.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-03-04 12:36 AM
Unpower and then power on.
https://community.se.com/t5/Gateways-and-Energy-Servers/replace-powertaglink-to-a-Panel-server/m-p/4...
I just have PowerTag Flex and it blink all time red even I take power off and then on. It won't go pairing mode.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-03-07 11:55 PM . Last Modified: 2024-10-15 02:47 AM
If device is not powered and you put power on. It will blink red slowly. You can't reconnect it to new server right a way. Device need to be powered until it start blink red rapidly and then reboot it to pairing mode.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.