Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-10-20 06:36 AM
Hi,
I have a costumer who has a PM5560 and a Masterpact with a Micrologic 5.0 E
I want to integrate the Masterpact to the PME, so I used a IFM interfase to connect the Masterpact to the PM5560, I did the connections acording to the following picture,
but when I push the IFM test button nothing happens, the management console does not recognize it.
What might I do?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-10-21 05:26 AM . Last Modified: 2021-10-21 05:52 AM
Dear @JuanMQT,
The PM5000 must be connected on the Modbus side (Modbus Master side) and not on the ULP side (breaker side) like an FDM121.
In this case, the PM5000 has to be connected to the Modbus TCP interface of the breakers (IFE).
It is very simple to make with Ethernet cable.
See diagram below in red on the right.
In this case, the wiring is a bit more complex.
It is done with the interface in red below by serializing the PM5000 with the IFMs
Here is an example of serial IFM connections:
You have to add the PM in series upstream or downstream of this "daisy chain".
Do not forget the termination resistor on the last device in the chain.
It is noted F on the diagram above or it is the small black square on the example of the PM5000 chain.
Feel free to ask if something is not clear.
Best regards
Ludovic
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-10-21 05:26 AM . Last Modified: 2021-10-21 05:52 AM
Dear @JuanMQT,
The PM5000 must be connected on the Modbus side (Modbus Master side) and not on the ULP side (breaker side) like an FDM121.
In this case, the PM5000 has to be connected to the Modbus TCP interface of the breakers (IFE).
It is very simple to make with Ethernet cable.
See diagram below in red on the right.
In this case, the wiring is a bit more complex.
It is done with the interface in red below by serializing the PM5000 with the IFMs
Here is an example of serial IFM connections:
You have to add the PM in series upstream or downstream of this "daisy chain".
Do not forget the termination resistor on the last device in the chain.
It is noted F on the diagram above or it is the small black square on the example of the PM5000 chain.
Feel free to ask if something is not clear.
Best regards
Ludovic