Masterpact NW16H1, Micrologic 5.0 E Unable to communicate with an IFM

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Masterpact NW16H1, Micrologic 5.0 E Unable to communicate with an IFM
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
71
J_Travostino
Sisko J_Travostino Sisko
70
S-W
Commander S-W Commander
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Solved
JuanMQT
Lieutenant JG JuanMQT
Lieutenant JG

Posted: ‎2021-10-20 06:36 AM

0 Likes
1
2121
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-20 06:36 AM

Masterpact NW16H1, Micrologic 5.0 E Unable to communicate with an IFM

Hi, 

I have a costumer who has a PM5560 and a Masterpact with a Micrologic 5.0 E

I want to integrate the Masterpact to the PME, so I used a IFM interfase to connect the Masterpact to the PM5560, I did the connections acording to the following picture,

 

 

Masterpact Micrologic.PNG

 

 

but when I push the IFM test button nothing happens, the management console does not recognize it.

What might I do?

Labels
  • Labels:
  • Connectivity
  • Products
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Ludovic_Soudril
Lieutenant JG Ludovic_Soudril Lieutenant JG
Lieutenant JG

Posted: ‎2021-10-21 05:26 AM . Last Modified: ‎2021-10-21 05:52 AM

2 Likes
0
2092
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-21 05:26 AM . Last Modified: ‎2021-10-21 05:52 AM

Dear @JuanMQT,

 

The PM5000 must be connected on the Modbus side (Modbus Master side) and not on the ULP side (breaker side) like an FDM121.

 

  • Either the communication is in Modbus TCP (Ethernet):

In this case, the PM5000 has to be connected to the Modbus TCP interface of the breakers (IFE).

It is very simple to make with Ethernet cable.

See diagram below in red on the right.

 

Image1.jpg

 

 

  • Either the communication is in serial Modbus:

In this case, the wiring is a bit more complex.

It is done with the interface in red below by serializing the PM5000 with the IFMs

 

Image2.jpg

 

 

Here is an example of serial IFM connections:

 

Image3.jpg

 

You have to add the PM in series upstream or downstream of this "daisy chain".

Do not forget the termination resistor on the last device in the chain.

It is noted F on the diagram above or it is the small black square on the example of the PM5000 chain.

 

 

Feel free to ask if something is not clear.

 

Best regards

Ludovic

 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Ludovic_Soudril
Lieutenant JG Ludovic_Soudril Lieutenant JG
Lieutenant JG

Posted: ‎2021-10-21 05:26 AM . Last Modified: ‎2021-10-21 05:52 AM

2 Likes
0
2093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-21 05:26 AM . Last Modified: ‎2021-10-21 05:52 AM

Dear @JuanMQT,

 

The PM5000 must be connected on the Modbus side (Modbus Master side) and not on the ULP side (breaker side) like an FDM121.

 

  • Either the communication is in Modbus TCP (Ethernet):

In this case, the PM5000 has to be connected to the Modbus TCP interface of the breakers (IFE).

It is very simple to make with Ethernet cable.

See diagram below in red on the right.

 

Image1.jpg

 

 

  • Either the communication is in serial Modbus:

In this case, the wiring is a bit more complex.

It is done with the interface in red below by serializing the PM5000 with the IFMs

 

Image2.jpg

 

 

Here is an example of serial IFM connections:

 

Image3.jpg

 

You have to add the PM in series upstream or downstream of this "daisy chain".

Do not forget the termination resistor on the last device in the chain.

It is noted F on the diagram above or it is the small black square on the example of the PM5000 chain.

 

 

Feel free to ask if something is not clear.

 

Best regards

Ludovic

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of