Posted: 2020-12-31 11:11 PM
I am needing to purchase a 750kVA transformer.
I've done all calculations for for my power consumption for 10 greenhouses. We will require a 750kVA transformer. I am needing to find one close to southern Oklahoma very quickly. OR I need suggestions for my setup. My actual load will be approximately 52,000 watts per green house X 10 plus additional load for travel trailers, probably around 3 of them. This is for a Medical Marijuana grow facility. Also, what kind of power will I need coming from the power company for such? Thank you in advance for any assistance.
James
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-02-09 12:22 AM
Hi Jacarpen,
Let me ask you some questions
1- Why one phase power transformer? Isn't it better to design 3 phase in order to distribute loads equally per phase?
2- For sustainability, It might be better to consider a spare transformer. or a backup power supply such as generator.
3-If you consider a spare, this might also be an opportunity for future in case the cannabis capacity is decided to be expanded.
Sincerely
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.

Posted: 2020-12-31 11:13 PM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-02-09 12:22 AM
Hi Jacarpen,
Let me ask you some questions
1- Why one phase power transformer? Isn't it better to design 3 phase in order to distribute loads equally per phase?
2- For sustainability, It might be better to consider a spare transformer. or a backup power supply such as generator.
3-If you consider a spare, this might also be an opportunity for future in case the cannabis capacity is decided to be expanded.
Sincerely