Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Posted: 2021-03-07 03:13 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-16 07:30 AM . Last Modified: 2021-03-17 12:57 AM
Hello @Anonymous user
There are several wiring schemes for star delta motor starters with different location for overload protection:
When the overload protection is located before the Star-Delta connection as in figure 1 and 2 the overload protection shall be adjusted according to the motor full load current at main system voltage
When the overload protection is located inside the delta as in figure 3, the overload protection shall be adjusted according to motor full load current at main system voltage divided by 1,732.
Does it answer your question ?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-15 07:29 AM . Last Modified: 2021-03-15 07:30 AM
up ⬆️
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-16 07:30 AM . Last Modified: 2021-03-17 12:57 AM
Hello @Anonymous user
There are several wiring schemes for star delta motor starters with different location for overload protection:
When the overload protection is located before the Star-Delta connection as in figure 1 and 2 the overload protection shall be adjusted according to the motor full load current at main system voltage
When the overload protection is located inside the delta as in figure 3, the overload protection shall be adjusted according to motor full load current at main system voltage divided by 1,732.
Does it answer your question ?