Compact NS current limiting curves
Hello,
I've received a question from a customer about current limiting curves for compact NS1250N breaker. In our catalogue we have a graph with representative curve. The question is how to read the graph for specific value of 24 kA current? Do we have a online tool maybe?
Best regards,
K
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-22 04:55 AM
hello @KrunoslavSever
Sorry I saw the question just today
As I know no tools exist to read them
Don't hesitate to ask this type of question to CCC
For 24kA we can read around 13.5kA. You must know this value are determined by simulation and calculation to help the panel board design. Nevertheless, at end panel builder need to plan a Icc test to validate the product integration.
Breaker Product Expert
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-04-23 02:29 AM
Also,
is it possible to see those curves in Ecodial? Currently, I can see only I-t curve in ecodial.
Thank you,
K
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-17 12:49 PM
For the graph, you just find where the 24 kA mark hits the curve and then check the values on the axes. As for an online tool, try looking on the manufacturer's website or give their support a shout. They usually have something that can help.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-22 04:55 AM
hello @KrunoslavSever
Sorry I saw the question just today
As I know no tools exist to read them
Don't hesitate to ask this type of question to CCC
For 24kA we can read around 13.5kA. You must know this value are determined by simulation and calculation to help the panel board design. Nevertheless, at end panel builder need to plan a Icc test to validate the product integration.
Breaker Product Expert