MTZ Restricted Earth Fault Protection.

Power Distribution and Digital

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Solved
Peter_Hall
Lt. Commander | EcoXpert Master Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master

MTZ Restricted Earth Fault Protection.

We are seeing a big rise in the number of enquiries for battery storage systems and renewables in general. there seems to be a big push (in the UK) for earth fault protection. We cover this with the ML4 trop units on NSX and M6.0X on MTZ. However there seems to be a growing requirement to have REF protection (earth fault protection looking back into the transformer secondary winding). 

 

Can anyone in the MTZ development team advise the time line to include this protection on the MTZ offer as previously offered on NW/NT? 

Tags (1)

Accepted Solutions
Ludovic_Soudril
Lieutenant JG Lieutenant JG
Lieutenant JG
1
2074

Re: MTZ Restricted Earth Fault Protection.

Hi Peter,

 

Restricted Earth Fault is not available today on MTZ.

 

REF is planned to be implemented in MTZ via a dedicated Digital Module in 2022.

 

Today, the only solution for REF on ACB is with NW (special configuration).

 

Best regards

Ludovic

See Answer In Context

Tags (1)
7 Replies 7
Kiran_Lagwankar
Ensign Ensign
Ensign
0
2107

Re: MTZ Restricted Earth Fault Protection.

In MTZ ACBs, Restricted Earth Fault protection is available as in MasterPact NW/NT. The terminology used is SGR (Source to Ground)protection. It involves external sensor( SGR Sensor) to measure the transformer Neutral current and MDGF Module.

 

Please refer our Detailed catalogue of MTZ for SGR protection.

 

Hope this answers your question.

 

Best Regards

Kiran Lagwankar 

Tags (1)
Fabien_Mastrot
Lieutenant Lieutenant
Lieutenant
0 Likes
5
2091

Re: MTZ Restricted Earth Fault Protection.

Hello Peter, you meant , designing a Masterpact MTZ with a 4 poles breakers but with no protection for Neutral inside the breaker ? Thanks 

 

Fabien Mastrot
EcoXpert global badge owner
Tags (1)
Peter_Hall
Lt. Commander | EcoXpert Master Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master
4
2090

Re: MTZ Restricted Earth Fault Protection.

Hi Fabien,

 

No, let me explain a bit clearer.

 

We are looking for an ACB with overcurrent protection. However we would also like to protect the cables & the transformer LV winding 'upstream' via and earth fault protection. Normally this is achieved by:

 

MTZ ACB with M2.0/5.0X trip unit.

Aveva (Was Alstom/GEC) MCAG14 relay with 4 x CT's, N/E link fitted downstream of the CT's (before the ACB).

Battery charger to trip the MTZ ACB Sht on relay operation.

 

The MCAG 14 CT's are the limit of the 'zone'. Therefore any earth fault occurring between the transformer LV winding and the CT's is detected and trips the ACB i.e. an in zone fault.

 

Hope that this makes sense?   

Tags (1)
Ludovic_Soudril
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
3
2084

Re: MTZ Restricted Earth Fault Protection.

Dear Peter,

 

Just to be 100% sure of your request.

 

Do you want to achieve with MTZ the same feature (Restricted Earth Fault Protection) as the one proposed with NW in the doc attached below?

 

Best regards

Ludovic

Attachments
Tags (1)
Peter_Hall
Lt. Commander | EcoXpert Master Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master
0 Likes
2
2080

Re: MTZ Restricted Earth Fault Protection.

Hi Ludovic,

 

That is exactly the application.

 

Best regards,

 

Peter Hall.

Tags (1)
Ludovic_Soudril
Lieutenant JG Lieutenant JG
Lieutenant JG
1
2075

Re: MTZ Restricted Earth Fault Protection.

Hi Peter,

 

Restricted Earth Fault is not available today on MTZ.

 

REF is planned to be implemented in MTZ via a dedicated Digital Module in 2022.

 

Today, the only solution for REF on ACB is with NW (special configuration).

 

Best regards

Ludovic

Tags (1)
Peter_Hall
Lt. Commander | EcoXpert Master Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master

Re: MTZ Restricted Earth Fault Protection.

Hi Ludovic,

 

That is great. Thank you for clarifying this.

 

Best regards,

 

Peter Hall.

Tags (1)