Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-10-20 03:37 PM . Last Modified: 2025-10-20 03:41 PM
Hi all,
I'm looking at NS800N Circuit breaker and I see the following technical info
Icu = 50KA / 400v
Icw = 19.2KA for 1 sec
Integrated instantaneous protection (peak) = 40KA
Now, if the peak is 40KA (which is expected, as it is 2.1*19.2), shouldn't that be a current limiting device?
Because when I look at current limiting curves, I can see that NS800N let-thru can go up to >100KA , In my mind it should peak at 40KA.
Can someone explain what am I missing here?
Just confused how all these 3 parameters link together?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-10-22 12:57 AM . Last Modified: 2025-10-22 01:06 AM
hello @MoBawy
NS800N is not a limiter bloc, even concerning the protection curve, it include an instantaneous protection witch give an automatic trip if current exceed Ii.
Icw is a theorical value (using just for certification test) never saw by breaker on reality to demonstrate the robusness of the product.