Can 2 different BMXDDO1602 Module outputs still be directly paralleled together if their respective cards are on different drops (without diodes)?

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Modicon PAC Forum
  • Can 2 different BMXDDO1602 Module outputs still be directly paralleled together if their respective cards are on different dr...
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
MatthewM
Lt. Commander MatthewM
8
RoozeeR
Lt. Commander RoozeeR Lt. Commander
7
Trinxs1
Lt. Commander Trinxs1 Lt. Commander
6
ciupol
Lieutenant ciupol
6
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Modicon PAC Forum
maks.chayun
maks.chayun Cadet
Cadet

Posted: ‎2025-04-03 10:55 AM

0 Likes
3
172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-03 10:55 AM

Can 2 different BMXDDO1602 Module outputs still be directly paralleled together if their respective cards are on different drops (without diodes)?

Say I wanted to implement a redundant I/O scheme where I paralleled two different BMXDDO1602 card outputs whose cards were located on two separate I/O drops (obviously on two different racks).

Assuming:
1) Their pre-actuator terminals were fed from the same power supply.

2) Both outputs are meant both be on or off simultaneously (no mixed states).

Could the outputs be paralleled together directly or would the output first have to go to two different diodes with their cathodes connected together?

 

I've read on the data sheet for the BMXDDO1602 that their outputs are parallelable (up to two), but I'm not sure if that was referring to outputs that were on the same card or not.

Labels
  • Labels:
  • 01. Modicon M340 PAC
  • 02. Modicon M580 ePAC
  • 04. Modicon X80 IO
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
dnordenberg1
Lieutenant dnordenberg1
Lieutenant

Posted: ‎2025-04-03 10:32 PM

0 Likes
0
144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-03 10:32 PM

99% sure it would not matter if it would be from another card. If you are unsure, take something like 1kohm resistor between an enabled output and a disabled and check the current. If the current is like 100 microamps or below then you are fine, it will not cause any harm to parallel the outputs, if it is towards 20mA it is shorting, then turn off.

Reply

Link copied. Please paste this link to share this article on your social media post.

GabrieleMicheli
GabrieleMicheli Cadet
Cadet

Posted: ‎2025-04-04 12:21 AM

0 Likes
0
129
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-04 12:21 AM

I suggest you take a look at these files, they are very interesting 🙂

Attachments
How Can I Implement redundant IO with Modicon M580.auto.sta.7z
Reply

Link copied. Please paste this link to share this article on your social media post.

ProfHameedi
Ensign ProfHameedi Ensign
Ensign

Posted: ‎2025-04-04 08:07 AM

0 Likes
0
109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-04 08:07 AM

If you look closely at the schematic circuit of the BMXDDO1602 module, you will see that the output terminals are the DRAIN pins of MOSFET transistors, so connecting (2) output pins together will not affect the internal circuit, especially the GATE circuits are different.

On the contrary, this scheme will enhance the operation and performance by Load Current sharing (Load Current will be divided by 2 pass through 2 transistors).

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of