Posted: 2024-06-06 05:41 PM
I am facing an "overload or shortcut to GND Status" issue on a BMXDDO0802S module installed on a RIO Chassis of the M580S.
The CPU part number is BMEH584040S.
This output is connected to a SIL3 Safety Relay from Phoenix Contact (Part Number: 2981020).
There are other channels connected to the same relay which work fine.
It is not possible to operate the output when this fault is present.
EcoStruxure Control Expert 15.2 is used.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-18 05:02 PM
If the T/B installed on the front of the card is connected to another BMXSDO card and the same phenomenon occurs, the cable connected to the T/B may be the problem.