Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
iEM3000 and Summing Transformer
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2025-07-1010:36 PM
iEM3000 and Summing Transformer
Hello Team,
Any experience with summing transformer ?
One of my customer wants to add summing transformer to connect to an energy counter.
Goal is to have one measurement point to have Power Delivered and Power Received (need a Modbus register to connect to a PLC in case of "Power Received" - no grid injection allowed).
Anyone has experienced this kind of config ?
Is it compatible with bidirectional power ?
Thanks for your help.
Romain POLETTE Solution Architect - France Operations
Link copied. Please paste this link to share this article on your social media post.
2025-07-1102:51 AM
Hi,
If the loads distributed on the two lines are symmetrical and equal, this setup will work more reliably and accurately. All current transformers connected to the summation CT must be exactly the same type and rating.
If the loads are not equal, I would recommend using two separate energy analyzers instead of this method.
That said, your diagram is correct for equal system. Summation current transformers are typically used to combine signals from multiple CTs and to scale the output current to a level suitable for energy analyzers.