Whole Number issue with Integrator Module

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Whole Number issue with Integrator Module
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
sesa261344
sesa261344 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2013-12-19 03:19 AM

0 Likes
4
978
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-12-19 03:19 AM

Whole Number issue with Integrator Module

Dear All,

In ION 7650 Power Logic Meter, the Integrator Module is calculating the KWH from KW Total. This KWH is displayed on the Meter with two decimal places, e.g 99999.XX

But, when we link the output of this Integrator module with a numeric element or any other module inside the Meter Framework, the value read is a whole number without decimal places.

E.g if you have 99999.XX, you will read only 99999 in Vista.

Even if you try to read the value on the output of this Integrator module, it is showing a whole number.

Any idea as to why this issue is appearing?

Regards.

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
jimbradley
Lt. Commander jimbradley
Lt. Commander

Posted: ‎2013-12-20 09:37 AM

0 Likes
0
891
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-12-20 09:37 AM

It depends on how the Modbus register is configured.  If the data is formatted to any of the following, U16,S16,U32,S32 then the data is integer only and any decimal value is lost (I'm not sure if it is rounded or truncated)

To "retain" the decimal you can apply scaling at the Modbus module level.  For example if you apply a x100 scale on the Modbus output then apply  / 100 to the register in the MDI or translator you "gain" of resolution.  This however can cause overflow if the original inpout value gets to big.

Jim

See Answer In Context

Reply
Replies 4
patrickw
Ensign patrickw Ensign
Ensign

Posted: ‎2013-12-19 11:16 AM

1 Like
2
891
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-12-19 11:16 AM

Hi Salman,

Is this meter being read via ION protocol, or modbus?

Reply
jimbradley
Lt. Commander jimbradley
Lt. Commander

Posted: ‎2013-12-19 12:39 PM

2 Likes
0
891
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-12-19 12:39 PM

The default Vista diagrams are set to display "0" digits after the decimal place on the Energy and Dmd screens.

You can change this by right clicking on the Vista object and selecting the "Display" tab of the "Numeric Object Configuration" window and changing the "Resolution" value to the desired number:

2894

Jim

Reply
sesa261355
sesa261355 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2013-12-19 09:23 PM

0 Likes
1
891
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-12-19 09:23 PM

The meter is reading on modbus protocol.the issue what we are facing is the output of the integrator module is a whole no (which should show me a decimal value ).when the value is being linked to a display screen. The value now shows in decimal. Any reason for this changeover?

Reply
jimbradley
Lt. Commander jimbradley
Lt. Commander

Posted: ‎2013-12-20 09:37 AM

0 Likes
0
892
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-12-20 09:37 AM

It depends on how the Modbus register is configured.  If the data is formatted to any of the following, U16,S16,U32,S32 then the data is integer only and any decimal value is lost (I'm not sure if it is rounded or truncated)

To "retain" the decimal you can apply scaling at the Modbus module level.  For example if you apply a x100 scale on the Modbus output then apply  / 100 to the register in the MDI or translator you "gain" of resolution.  This however can cause overflow if the original inpout value gets to big.

Jim

Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of