What is the cause of getting a negative reading for the active power (W) in powerlogic PM21000, and how i can to change the mode from export to import
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
There could be many reasons why you are seeing negative power. The most common reason is CTs are installed backwards, the next most common reason is the CTs and voltage connections are not on the same phase. Example: A phase voltage however B phase CT.
Suggest looking at the phase angles between voltage and current to determine if you have a wiring issue.
There could be many reasons why you are seeing negative power. The most common reason is CTs are installed backwards, the next most common reason is the CTs and voltage connections are not on the same phase. Example: A phase voltage however B phase CT.
Suggest looking at the phase angles between voltage and current to determine if you have a wiring issue.