Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Sag / Swell ?? / Transient ??? / What do you think?

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Sag / Swell ?? / Transient ??? / What do you think?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
581
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2015-07-09 12:37 AM

0 Likes
7
4228
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-07-09 12:37 AM

Sag / Swell ?? / Transient ??? / What do you think?


Hello

I do not speak English well.

I have a question for you.

I think Sag / Swell.

Why Transient ??

Module has not changed

Thanks!


Attachments
Tags (2)
  • Tags:
  • pme
  • power_monitoring_expert
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
jbickel
jbickel Leader
Leader

Posted: ‎2015-07-10 07:47 AM

0 Likes
0
4079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-07-10 07:47 AM

Now that is the magic question...

Based on the information provided, all that can authoritatively be said is that it's a single-phase event lasting approximately 5 cycles. Determining the actual cause of the event would require a lot more data and contextual information.

See Answer In Context

Reply
Replies 7
jbickel
jbickel Leader
Leader

Posted: ‎2015-07-09 07:31 AM

0 Likes
6
4079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-07-09 07:31 AM

Based on the image you have provided and the definition provided by recognized PQ standards, it is a voltage sag event. A good rule of thumb is that transients are one cycle or less. In this case, the term "transient" is misleading.

Reply
DanL
DanL Champion
Champion

Posted: ‎2015-07-09 10:50 AM

0 Likes
3
4079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-07-09 10:50 AM

Assuming this is from an ION meter, the "transient" terms are comming from the ION Transient Module. Either the querry filter (ALARM2.jpg) is hiding the Sag events generated by the SagSwell module, or perhaps the SagSwell module is mis-configured. As far as I know the default configuration of ION templates with a transient module is to disable the transient module during sag/swell events. Also possible is that the transient module's waveshape comparing algorithm detected the leading edge of the disturbance before the RMS level fell below the sag/swell module's threshold.

Reply
jbickel
jbickel Leader
Leader

Posted: ‎2015-07-09 12:58 PM

0 Likes
2
4079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-07-09 12:58 PM

The device is providing Disturbance Direction Detection information for this particular event. I know the old PowerLogic devices (CM4000/CM3350) only provided DDD information for events classified as sags or swells (for various reasons that are not pertinent to this discussion). Out of curiosity, does the ION device provide DDD information for events classified as transient events?

But back to the original question...the textbook definition of this event is that it's a voltage sag.

Reply
DanL
DanL Champion
Champion

Posted: ‎2015-07-09 01:42 PM

0 Likes
1
4079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-07-09 01:42 PM

The DDD module source inputs are expected to be from at least the sag/swell module and optionally the transient module ("transient" detection and measurement on the ION module differs dramatically from the CM4000T transient feature). For example the ION7550 and PM8000 support SagSwell and DDD, but not transients.

The SagSwell module, transient module, and DDD modules operate independantly unless configured otherwise by linking enable/disable logic in the template. It looks like the DDD module allows any input trigger to start the capture and evaluation of waveform data to compute the direction and confidence.

Yes I agree the waveform depicts a classical voltage sag, but the event log indicates the event was detected (at least) by the transient module. Sorry about the confusion.

Dan

Reply
Anonymous user
Not applicable

Posted: ‎2015-07-09 06:57 PM

0 Likes
1
4079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-07-09 06:57 PM


Thank you.

Sowhydidthis phenomenonappear?

Reply
jbickel
jbickel Leader
Leader

Posted: ‎2015-07-10 07:31 AM

0 Likes
0
4079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-07-10 07:31 AM

Dan - Would like to talk to you offline sometime about some of the potential issues of performing DDD on transients (at your discretion).

Reply
jbickel
jbickel Leader
Leader

Posted: ‎2015-07-10 07:47 AM

0 Likes
0
4079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-07-10 07:47 AM

Now that is the magic question...

Based on the information provided, all that can authoritatively be said is that it's a single-phase event lasting approximately 5 cycles. Determining the actual cause of the event would require a lot more data and contextual information.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore