Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Important Announcement: Community Back to Full Functionality

Dear Members, we are thrilled to announce that our Community is back to full functionality and that posts publication is now enabled again! We appreciate your patience during the last weeks. Learn more about our Community Guidelines. Thank you, Schneider Electric Community Team.

Sag / Swell ?? / Transient ??? / What do you think?

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Sag / Swell ?? / Transient ??? / What do you think?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
299
Ramasamy_N
Commander Ramasamy_N Commander
75
DanL
Captain DanL Captain
72
Robert_Lee
Captain Robert_Lee Captain
67
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
skkim_isama_net
Lieutenant | EcoXpert Master skkim_isama_net Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2015-07-09 12:37 AM

0 Likes
7
1044
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-07-09 12:37 AM

Sag / Swell ?? / Transient ??? / What do you think?


Hello

I do not speak English well.

I have a question for you.

I think Sag / Swell.

Why Transient ??

Module has not changed

Thanks!


Attachments
Tags (2)
  • Tags:
  • pme
  • power_monitoring_expert
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
jbickel
Ensign jbickel
Ensign

Posted: ‎2015-07-10 07:47 AM

0 Likes
0
895
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-07-10 07:47 AM

Now that is the magic question...

Based on the information provided, all that can authoritatively be said is that it's a single-phase event lasting approximately 5 cycles. Determining the actual cause of the event would require a lot more data and contextual information.

See Answer In Context

Reply
Replies 7
jbickel
Ensign jbickel
Ensign

Posted: ‎2015-07-09 07:31 AM

0 Likes
6
895
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-07-09 07:31 AM

Based on the image you have provided and the definition provided by recognized PQ standards, it is a voltage sag event. A good rule of thumb is that transients are one cycle or less. In this case, the term "transient" is misleading.

Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2015-07-09 10:50 AM

0 Likes
3
895
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-07-09 10:50 AM

Assuming this is from an ION meter, the "transient" terms are comming from the ION Transient Module. Either the querry filter (ALARM2.jpg) is hiding the Sag events generated by the SagSwell module, or perhaps the SagSwell module is mis-configured. As far as I know the default configuration of ION templates with a transient module is to disable the transient module during sag/swell events. Also possible is that the transient module's waveshape comparing algorithm detected the leading edge of the disturbance before the RMS level fell below the sag/swell module's threshold.

Reply
jbickel
Ensign jbickel
Ensign

Posted: ‎2015-07-09 12:58 PM

0 Likes
2
895
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-07-09 12:58 PM

The device is providing Disturbance Direction Detection information for this particular event. I know the old PowerLogic devices (CM4000/CM3350) only provided DDD information for events classified as sags or swells (for various reasons that are not pertinent to this discussion). Out of curiosity, does the ION device provide DDD information for events classified as transient events?

But back to the original question...the textbook definition of this event is that it's a voltage sag.

Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2015-07-09 01:42 PM

0 Likes
1
895
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-07-09 01:42 PM

The DDD module source inputs are expected to be from at least the sag/swell module and optionally the transient module ("transient" detection and measurement on the ION module differs dramatically from the CM4000T transient feature). For example the ION7550 and PM8000 support SagSwell and DDD, but not transients.

The SagSwell module, transient module, and DDD modules operate independantly unless configured otherwise by linking enable/disable logic in the template. It looks like the DDD module allows any input trigger to start the capture and evaluation of waveform data to compute the direction and confidence.

Yes I agree the waveform depicts a classical voltage sag, but the event log indicates the event was detected (at least) by the transient module. Sorry about the confusion.

Dan

Reply
skkim_isama_net
Lieutenant | EcoXpert Master skkim_isama_net Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2015-07-09 06:57 PM

0 Likes
1
895
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-07-09 06:57 PM


Thank you.

Sowhydidthis phenomenonappear?

Reply
jbickel
Ensign jbickel
Ensign

Posted: ‎2015-07-10 07:31 AM

0 Likes
0
895
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-07-10 07:31 AM

Dan - Would like to talk to you offline sometime about some of the potential issues of performing DDD on transients (at your discretion).

Reply
jbickel
Ensign jbickel
Ensign

Posted: ‎2015-07-10 07:47 AM

0 Likes
0
896
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-07-10 07:47 AM

Now that is the magic question...

Based on the information provided, all that can authoritatively be said is that it's a single-phase event lasting approximately 5 cycles. Determining the actual cause of the event would require a lot more data and contextual information.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc