Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Regarding the split phase settings of HDPM6000

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Regarding the split phase settings of HDPM6000
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
T.Okada
T.Okada
Contributor

Posted: ‎2025-11-04 07:09 PM

0 Likes
4
1047
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-04 07:09 PM

Regarding the split phase settings of HDPM6000

Hi,

 

I have a question about the settings of HDPM6000.


I believe that to set single-phase three-wire in HDPM, you can select Split Phase under the General Settings tab. However, how should we configure branch circuits that take voltage from R-T (i.e., circuits using R-T for voltage)?

On the HDPM web interface, the Exp Phase options only allow selecting 1, 2, 3, or N, which seems to only support cases where voltage is taken from the N line. How should we configure for circuits that take voltage from R-T?

 

Thank you,

@T.Okada 

Labels
  • Labels:
  • HDPM6000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2025-11-07 08:37 AM

0 Likes
1
975
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-07 08:37 AM

Hi @T.Okada 

 

You're welcome.

 

You're correct. If each circuit using R-T voltage in Split Phase mode is monitored with two CTs (one on R and one on T), then the METSEHDPM6R84 would be required to support 42 such circuits. The METSEHDPM6R42 only supports up to 21 circuits in this configuration.

 

Also, just to clarify a point from my previous note. When configuring branch circuits in Split Phase mode that use R-T voltage, it's better to assign the CTs to Phase 1 and Phase 2, rather than Phase 1 and Phase 3, since using Phase 3 would misrepresent the electrical configuration.


While the HDPM calculates line-to-line voltage internally based on the Split Phase supply type, using Phase 1 and Phase 2 aligns with the expected configuration and helps maintain consistency with documentation.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

See Answer In Context

Reply
Replies 4
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2025-11-05 11:08 AM . Last Modified: ‎2025-11-05 12:30 PM

0 Likes
1
1027
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-05 11:08 AM

Hi @T.Okada 

 

As mentioned in HDPM6000 Installation guide:

Mehran_Mehrnia_0-1762365364941.png

If you have single-phase three-wire coming from a center-tapped transformer (the two hot legs are 180° apart), choose Split supply type.


If you have single-phase three-wire coming from two legs of a Wye transformer (which are 120° apart), you need to choose Wye supply type, because the electrical characteristics match a Wye system (120° phase difference, not 180°).

 

For circuits using R-T voltage in Split Phase mode, configure the branch circuit with two CTs, assign them to Phase 1 and Phase 3, and group them together into one circuit. The HDPM will calculate line-to-line voltage (R-T) internally based on the Split Phase supply type.

 

Mehran_Mehrnia_0-1762370818312.png

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
T.Okada
T.Okada
Contributor

Posted: ‎2025-11-06 06:58 PM

0 Likes
0
989
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-06 06:58 PM

Hi @Mehran_Mehrnia,

 

 

Thank you for your reply.

 

I understand the configuration for circuits using the R‑T voltage in split‑phase mode.

So, if I would like to configure a 42‑circuit system using the R‑T voltage in split‑phase mode, I would need to use the METSEHDPM6R84 (not the METSEHDPM6R42). Is my understanding correct?

 

Best regards,
Okada

Reply
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2025-11-07 08:37 AM

0 Likes
1
975
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-07 08:37 AM

Hi @T.Okada 

 

You're welcome.

 

You're correct. If each circuit using R-T voltage in Split Phase mode is monitored with two CTs (one on R and one on T), then the METSEHDPM6R84 would be required to support 42 such circuits. The METSEHDPM6R42 only supports up to 21 circuits in this configuration.

 

Also, just to clarify a point from my previous note. When configuring branch circuits in Split Phase mode that use R-T voltage, it's better to assign the CTs to Phase 1 and Phase 2, rather than Phase 1 and Phase 3, since using Phase 3 would misrepresent the electrical configuration.


While the HDPM calculates line-to-line voltage internally based on the Split Phase supply type, using Phase 1 and Phase 2 aligns with the expected configuration and helps maintain consistency with documentation.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
T.Okada
T.Okada
Contributor

Posted: ‎2025-11-11 12:10 AM . Last Modified: ‎2025-11-11 12:11 AM

0 Likes
0
932
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-11 12:10 AM

Hi @Mehran_Mehrnia 

 

Thank you for your reply!

I understand the configuration of the HDPM6000.

 

Best Regards,

Okada

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore