Hi,
Guide me in understanding the ride though time and sag correction capability of Dynamic voltage restorer DVR30060400M.
In the datasheet it is mentioned that the Sag correction capability - for 3 phases 60 % for 30s and in the same datasheet it is mentioned that the ride through time - 40 ms.
When the DVR can compensate the sag of 60% for 30s, the ride through time achieved is 30s, but in datasheet ride through is mentioned as 40ms. Please clarify what is the difference between sag correction capability and ride through time ?
Query : for the voltage sag /dip of 55% (i.e. 45% voltage remaining) with the sag duration of 80ms. Whether this sag can be mitigated/ride through with this Dynamic Voltage Restorer?
Link copied. Please paste this link to share this article on your social media post.
Dear Srakesh,
Based on the datasheet I provided, the DVR system with DVR30060400M is capable of compensating for a 60% three-phase voltage sag for up to 30 seconds. You can also find this information in the Technical Specifications section, where the SAG correction capability is specified as-40% to -60% (depending on the range) for 30 seconds.
Regarding your other question:
For a voltage sag/dip of 55% (i.e. 45% voltage remaining) with a sag duration of 80 ms, can this sag be mitigated/ridden through by the Dynamic Voltage Restorer?
The answer is yes. For the 300 kVA / 60% sag configuration, a 55% voltage sag lasting 80 ms is within the specified sag correction capability, provided that the connected load is within the rated capacity of 300 kVA.
As for the“ride-through – 40 ms” value you mentioned, I could not find this specification in the datasheet. If you could share the original document or the relevant section where the 40 ms requirement is stated, I would be able to better understand its exact meaning and assess it against the DVR specifications.
Best regards,
Yan
Link copied. Please paste this link to share this article on your social media post.
Dear Srakesh,
Based on the datasheet I provided, the DVR system with DVR30060400M is capable of compensating for a 60% three-phase voltage sag for up to 30 seconds. You can also find this information in the Technical Specifications section, where the SAG correction capability is specified as-40% to -60% (depending on the range) for 30 seconds.
Regarding your other question:
For a voltage sag/dip of 55% (i.e. 45% voltage remaining) with a sag duration of 80 ms, can this sag be mitigated/ridden through by the Dynamic Voltage Restorer?
The answer is yes. For the 300 kVA / 60% sag configuration, a 55% voltage sag lasting 80 ms is within the specified sag correction capability, provided that the connected load is within the rated capacity of 300 kVA.
As for the“ride-through – 40 ms” value you mentioned, I could not find this specification in the datasheet. If you could share the original document or the relevant section where the 40 ms requirement is stated, I would be able to better understand its exact meaning and assess it against the DVR specifications.
Best regards,
Yan