Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

RD96 on PM8000 Downloading Error

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • RD96 on PM8000 Downloading Error
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
dsantillan
dsantillan
Contributor

Posted: ‎2023-08-29 08:02 AM

0 Likes
5
3420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-08-29 08:02 AM

RD96 on PM8000 Downloading Error

Hello, 

 

We recently installed a PM8244 meter with RD96 display. 

 

PM8000 firmware 004.000.000

 

Upon connection of the RD96 the screen reads Downloading Application 004 003 007

After a few minutes it changes to Downloading Error and the Display cannot be operated. 

 

How can this be corrected?

 

Thank you. 

 

 

 

 

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2023-08-30 07:59 AM

0 Likes
1
3378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-08-30 07:59 AM

Hello @dsantillan ,

 

When you connect to the meter with ION Setup or PME, there is a module called Factory. One of the output registers of this module is RMD serial number and RMD version. If the meter does not have this information it indicates that meter is not able to talk to the display.

 

The "system" has 3 parts, the meter, the display and the cable between display and meter. Hard to say if a specific one of these is misbehaving. If you have other meters with working displays it may be possible to switch 1 item at a time to test that item. For example start with cable, if both cables work with the reference test, then not the cable. Then try switching the displays. If the error follows the display, would suggest something happening with the display. If error follows meter, would suggest something happening with the meter.

Are you able to do such a test?

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 5
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2023-08-29 01:14 PM

1 Like
3
3415
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-08-29 01:14 PM

Hello @dsantillan ,

Is the display also new? Are you able to communicate with the Meter? can meter read serial number of display?

Do you know firmware version of the display? (Display ad meter each have unique firmware).

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
dsantillan
dsantillan
Contributor

Posted: ‎2023-08-29 08:52 PM

0 Likes
2
3407
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-08-29 08:52 PM

Hello Charles, 

 

Thank you for the reply. 

 

Yes, these are new were bought as PM8244. The box had the PM8000 and the RD96 in it. 

Yes, PME read the meters them just fine. I can also access via IONSetup. 

The meter does not read anything from the display. 

Please find images from the display attached. 

 

Attachments
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2023-08-30 07:59 AM

0 Likes
1
3378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-08-30 07:59 AM

Hello @dsantillan ,

 

When you connect to the meter with ION Setup or PME, there is a module called Factory. One of the output registers of this module is RMD serial number and RMD version. If the meter does not have this information it indicates that meter is not able to talk to the display.

 

The "system" has 3 parts, the meter, the display and the cable between display and meter. Hard to say if a specific one of these is misbehaving. If you have other meters with working displays it may be possible to switch 1 item at a time to test that item. For example start with cable, if both cables work with the reference test, then not the cable. Then try switching the displays. If the error follows the display, would suggest something happening with the display. If error follows meter, would suggest something happening with the meter.

Are you able to do such a test?

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2023-08-30 03:57 PM

0 Likes
0
3375
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-08-30 03:57 PM

Make sure the display cable is plugged into the RMD port on the base unit (and not to the Ethernet TCP ports on the bottom side of the base unit).  The cable you are using should also support PoE (Power over Ethernet)  and should be connected directly to the base unit and not though any type of IT equipment like a router and/or switch.

Reply
dsantillan
dsantillan
Contributor

Posted: ‎2023-09-19 04:39 PM

1 Like
0
3307
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-09-19 04:39 PM

Hello Charles, 

 

Thank you for the input. For this specific case, new patch cords were required, and then a power cycle of the units. 

 

Best regards, 

 

Douglas

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore