Dear All,
Kindly share your experience/ideas if have any one with me regarding Quantum PLC Ethernet communication with Power Logic ION88800/7650 Meter to read Electrical Parameters such as Volts, Amperes, Power, Power Factor and Frequency.
Using following Hardware.
1) 140CPU67160
2) 140NOE77111
3) TCSESM063F2CS1 Ethernet Switch
Using following Software.
1) Unity Pro XL 8.0
For your ref. i attached created logic snapshot.
Waiting your kind response.
Best Regards,
Rashid Mahmood
Posted: 2016-07-13 06:23 AM
Link copied. Please paste this link to share this article on your social media post.
I believe you are communicating ION Meter on Modbus TCP.
There is Ethernet IO scanner option in unity software under NOE tab use it its very easy to read modbus TCP devices.
BR
Genjua
Link copied. Please paste this link to share this article on your social media post.
Dear Waqas,
Thanks for your answer,
I tried with IO Scanner but in vain. I defined IP address an subnet mask ION 7650 network set up. Please let me know if in ION7650 meter there is other setting.
Best Regards,
Rashid Mahmood
Posted: 2016-07-18 09:46 AM
Link copied. Please paste this link to share this article on your social media post.
please share IO scanner screen shot here.
can you read the ION meter values on modbus tcp scanner? Modscan32?
BR
Genjua
Link copied. Please paste this link to share this article on your social media post.
TCP Port of 502 ?
Link copied. Please paste this link to share this article on your social media post.
YES TCP Port 502
Link copied. Please paste this link to share this article on your social media post.
Yes i can you read the ION meter values on modbus tcp scanner.
Please find the IO Scanner Screen shot with modbus tcp scanner..
Best Regards,
Rashid Mahmood
Link copied. Please paste this link to share this article on your social media post.
Thanks to all for your support and interest.
I would like to inform you that my query is solved and now ION meter communication with NOE module.
For you ref. see the attached snap shoot.