Can anyone advise if the Rope type CT of Powertag is immuned from electrical noise?
We are installing the CT inside an electrical trunking where a lot of electrical cables will be around.
Link copied. Please paste this link to share this article on your social media post.
Hello @RWG924,
The term electrical noise can be difficult to translate into something factual. The PowerTag Rope complies with the requirements defined in IEC 61557-12. However, the question specifically concerns crosstalk, which is not clearly defined in current standards.
The PowerTag Rope current sensor is specified to tolerate no more than a 0.4% deviation in its measurement due to interference from a neighboring wire. To minimize external influences, we recommend avoiding the placement of external wires near the closing block, as illustrated in the instruction sheet and as @Mehran_Mehrnia has already mentioned.
Best Regards,
JD
Link copied. Please paste this link to share this article on your social media post.
Hi @RWG924
PowerTag Rope is a Rogowski solution, which relies on measuring the rate of change of current (di/dt) which is different from conventional CTs that use magnetic cores. This makes them sensitive to external magnetic fields, however there are some Installation Best Practices:
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
Hello @RWG924,
The term electrical noise can be difficult to translate into something factual. The PowerTag Rope complies with the requirements defined in IEC 61557-12. However, the question specifically concerns crosstalk, which is not clearly defined in current standards.
The PowerTag Rope current sensor is specified to tolerate no more than a 0.4% deviation in its measurement due to interference from a neighboring wire. To minimize external influences, we recommend avoiding the placement of external wires near the closing block, as illustrated in the instruction sheet and as @Mehran_Mehrnia has already mentioned.
Best Regards,
JD
Link copied. Please paste this link to share this article on your social media post.
Thx JD. Do we have any documentation quoting the 0.4% deviation max limit due to cross talk even it is installed in a highly conductive influence trunking?
Many thx
Link copied. Please paste this link to share this article on your social media post.
Hello,
That is our internal specification for the current sensor on the rope. We can prepare a declaration that can be shared with you. However, we need to clarify which parameter is of interest to you (e.g., current, power, etc.).
Best regards,
JD
Link copied. Please paste this link to share this article on your social media post.
Many thanks. We need this document for a transportation customer. They concern with the Current and Power accuarcy. So for the Power accuracy , it is still limited at 0.4%; the same as current?
Link copied. Please paste this link to share this article on your social media post.
@Jesus_Diaz Please let me know the duration to get this 0.4% certificates for Power and Current.
Many thanks