Hello.
I have more PowerTags and one PowerTag Link.
In web page of PowerTag Link there are some preconfigured alarms.
For example: Current Alarm 45% of the Nominal Current.
I deleted all alarms from settings --> alarms.
No alarms should be triggered, but this (> 45%) alarm still appears.
Any idea how to disable this?
Best regards, Boris.
Link copied. Please paste this link to share this article on your social media post.
Hello,
This 45 % alarm is available in the bit 3 of the modbus register 3300.
I have made a test in my lab and also observe the bug that you mention with the last fw available 2.1.5
Unfortunately, you are rigth : It is possible to disable the 0%,50%, 80% current alarm in the alarm settings but the 45% current alarm cannot be disabled and alway appears in web page !
I will push the bug to the R&D team
BR
Link copied. Please paste this link to share this article on your social media post.
Hello @Boris_Horvat ,
What is the Firmware version of your PowerTag Link ?
Please go under SETTINGS -> DEVICES --> WIRELESS DEVICES.
Then check the following settings for your PowerTag Sensors:
Ensure that this setting is matching your breaker current rating.
Regards,
Link copied. Please paste this link to share this article on your social media post.
Hello @Romain_Polette.
FW version of PowerTag Link is 002.001.005.
Associate Breaker Rating is correctly set.
But the problem is, that there is no defined alarm, but "Current Alarm 45% of the Nominal Current" triggered all the time.
Best regards.
Link copied. Please paste this link to share this article on your social media post.
Hello,
This 45 % alarm is available in the bit 3 of the modbus register 3300.
I have made a test in my lab and also observe the bug that you mention with the last fw available 2.1.5
Unfortunately, you are rigth : It is possible to disable the 0%,50%, 80% current alarm in the alarm settings but the 45% current alarm cannot be disabled and alway appears in web page !
I will push the bug to the R&D team
BR
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Recently I also received feedback from a customer regarding this problem. Wondering do you have any updates from R&D? Thank you
Best regards,
Link copied. Please paste this link to share this article on your social media post.
Hello @Stuart_Cheng ,
R&D is actively working on the topic.
I will have more information soon.
Regards,
Link copied. Please paste this link to share this article on your social media post.
I forgot something important.
With PME you have the possibility to deactivate the 45% alarm. This workaround is not possible for the "Zero Current" Alarm.
Please go on system\translators => copy all PowerTagxxx.ion and .xml files.
Past them on config\translators
Go on system\translators\events => copy PowerTag.evt
Past the .evt file on config\translators\events
Open the config\translators\events\PowerTag.evt file with a text editor.
Check the line: <EventInfo ID="2502" Priority="128" Enabled="YES" Comment="Current Alarm (45%)" />
Change the parameter to Enables = "NO"
Restart ION Network Router and associated Services.
Restart ION Application Modules Services.
Regards,
Link copied. Please paste this link to share this article on your social media post.
Thanks for your information and please let me know if you have any updates from R&D. Thank you.
Best regards,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hello @Anirban ,
Any plan to integrate the "zero current" alarm on the PowerTag.evt file ?
This needs to be taken in account because we may face some complains in the futur with PowerTag + Panel Server.
Panel Server does not offer the feature to disable Modbus TCP Alarms (unlike PowerTag Link).
Thanks !