PowerTag A9MEM1521/22 measurements

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Re: PowerTag A9MEM1521/22 measurements
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
521
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
134
Ramasamy_N
Captain Ramasamy_N Captain
115
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
sesa453448_brid
Ensign sesa453448_brid Ensign
Ensign

Posted: ‎2020-07-21 05:29 PM . Last Modified: ‎2021-04-26 01:04 AM

0 Likes
5
2342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-21 05:29 PM

PowerTag A9MEM1521/22 measurements

Hi Guys,

 

I can't find information about the measurement capabilities of the N-Terminal of PowerTag A9MEM1521/22, are the same as the phase-Terminal?. We're planning to use these PowerTag references for a 2-phase system, any other ideas? is better to use 2 A9MEM1520 instead?

 

Thanks!!! 🙂

 

 

Labels
  • Labels:
  • PowerTag Energy
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2020-07-21 11:14 PM

1 Like
4
2339
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-21 11:14 PM

Hello @sesa453448_brid , 

 

Can you precise your architecture ?
N Terminal for any PowerTag Sensor has no CT. It is only used as a Voltage Reference so you cannot monitor any current on the Neutral.

If I understand your system will be : N, L1, L2 (No L3 ?). If you plan to use A9MEM1521/22 => it means that you have Acti 9 MCB. Can you give me the commercial ref of the breakers ?

Depending on your answer I may suggest you some configuration.


Thanks.

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 5
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2020-07-21 11:14 PM

1 Like
4
2340
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-21 11:14 PM

Hello @sesa453448_brid , 

 

Can you precise your architecture ?
N Terminal for any PowerTag Sensor has no CT. It is only used as a Voltage Reference so you cannot monitor any current on the Neutral.

If I understand your system will be : N, L1, L2 (No L3 ?). If you plan to use A9MEM1521/22 => it means that you have Acti 9 MCB. Can you give me the commercial ref of the breakers ?

Depending on your answer I may suggest you some configuration.


Thanks.

Romain POLETTE
Solution Architect - France Operations
Tags (1)
  • Tags:
  • english
Reply
marco_arias_ssm
marco_arias_ssm
Cadet

Posted: ‎2020-09-21 06:43 PM

0 Likes
3
2312
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-21 06:43 PM

Hello Romain

I want to conect A9MEM1570 in L1-L2-L3 system (No N). Will be any problem if i no conect the N terminal of powertag?

 

Regards

Tags (1)
  • Tags:
  • english
Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2020-09-22 10:27 PM

0 Likes
2
2307
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-22 10:27 PM

Hello @marco_arias_ssm , 

 

If you have a 3ph system without Neutral : it is more recommended to connect a A9MEM1573.

 

If you use the A9MEM1570 and if your system is balanced : your measurement precision will not be affected. But.... what are you going to do with the N pin of the PowerTag 1570 ?

 

Keep in mind that 1570 is dedicated for 3P+N unbalanced system. Neutral will improve the precision of the Power measurement.

 

Regards.

Romain POLETTE
Solution Architect - France Operations
Tags (1)
  • Tags:
  • english
Reply
marco_arias_ssm
marco_arias_ssm
Cadet

Posted: ‎2020-09-23 05:39 PM

0 Likes
1
2303
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-23 05:39 PM

Thanks Romain

I ask about the A9MEM1575 reference. I only see the A9MEM1570 in stock.

 

Regards

Tags (1)
  • Tags:
  • english
Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2020-09-23 10:04 PM . Last Modified: ‎2020-09-23 10:05 PM

1 Like
0
2301
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-23 10:04 PM

Hello @marco_arias_ssm , 

 

A9MEM1575 does not exists. I mentioned A9MEM1573 in my previous comment.

 

Please refer to the selection guilde.

Regards.

Romain POLETTE
Solution Architect - France Operations
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore