PowerLogicTM VL series- Modbus Setup
Hello All,
We have done a small modification to the Modbus parameter setting. Modbus parameters must be configured through the expert setup menu in section 700 (see PowerLogic™ User manual paragraph 5).
• BAUD RATE (701): the valid range is 1200 - 115200 baud. Default value = 19200. • PARITY (702): parity to be None, Even or Odd. Default value = Even. Note:For PARITY = None, use 2 bits stop. For PARITY = Even or Odd, use only 1 bit stop.
In general if Parity was set as Even or Odd then set as ----> 1- bit stop
But if the Parity was set as Noe then set as----> 2 bit stop
• SLAVE ADDRESS (703): the valid range is 1 - 247. Default value = 1.
The settings for baud rate and parity must be the same for all bus devices, the address must be unique for each device.