Dear Team,
We are facing one issue in PM2230. Where meter is configured for Over voltage tripping purpose. Meter is working fine and tripping breaker at set point. However it takes long time to reset.
Do we have any setting to reduce reset time.
What could be other possible reasons for such behaviour.
Link copied. Please paste this link to share this article on your social media post.
Hello @Chiragshah
Simulated this over voltage alarm behavior and the assigned relay turns OFF when the voltage drops below the dropout limit. There is no delay observed for the reset.
Please check if any delay time configured for dropout.
FYI, PM2230 relays are not recommended for tripping application due to the update time.
Regards,
Ramasamy N
Link copied. Please paste this link to share this article on your social media post.
Hello @Chiragshah
Simulated this over voltage alarm behavior and the assigned relay turns OFF when the voltage drops below the dropout limit. There is no delay observed for the reset.
Please check if any delay time configured for dropout.
FYI, PM2230 relays are not recommended for tripping application due to the update time.
Regards,
Ramasamy N
Link copied. Please paste this link to share this article on your social media post.
Thank you Ramasamy for information. Will check for any delay.