Bonjour,
Je dois configurer une sortie 4-20mA sur un PM8000. (image de la puissance active)
J'ai un module METSEP89M0024
Si quelqu'un a déjà fait ce genre de configuration via IONSETUP je suis preneur.
Merci d'avance,
Olivier
Link copied. Please paste this link to share this article on your social media post.
J'ai réussi à configurer ma sortie dans Analog Out Modules, je partage ma configuration.
le 693 correspond à 693kVA pour 20mA (TI 1000A)
Link copied. Please paste this link to share this article on your social media post.
J'ai réussi à configurer ma sortie dans Analog Out Modules, je partage ma configuration.
le 693 correspond à 693kVA pour 20mA (TI 1000A)