Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Power quality analysis : THD, thd, TDD

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Power quality analysis : THD, thd, TDD
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2014-03-24 01:34 AM

1 Like
5
8175
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-03-24 01:34 AM

Power quality analysis : THD, thd, TDD

Hi,

Do we have document where detailed explanation of THD, thd, TDD is available with its End user benefits.

How do we take advantage of this feature compared to competition.

Regards,

Chetan Dhake.

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
mrsrinivas
mrsrinivas Leader
Leader

Posted: ‎2014-04-24 06:58 AM

1 Like
0
8037
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-04-24 06:58 AM

Hi Chetan,

1) About THD, TDD:

  • TDD                           =     Total Demand Distortion of current.
  • THDI% (or thdi%)      =     Total Harmonic distortion of current.

The reason for above two terminologies as below:

THDI is the ratio of Harmonic current magnitude to Fundamental Current.

  1. i.e. THDI %      =      Ih / I1 x 100.

As the load (or I1)  varies, the ratio (THDI%) will also vary. This makes things complicated to arrive at specific limit of harmonic current. Hence TDD is used as a limiting factor for harmonic current distortion.

TDD             =     Ih / Imax x 100.

Where,

Imax     =     the current at Maximum Demand measured (or calculated) at the Point of Common coupling (PCC).

(PCC can be either Utility metering point or secondary of transformer.)

2) Measurement of THD, TDD:

THDI% can be measured by directly connecting harmonic analyzer or any THD measurable instrument.

But, in most of the situation it may be difficult to measure TDD, as TDD has to be measured at Maximum Demand scenario, hence TDD will be calculated based on THDI% measurement and Maximum Demand data from customer.

3) Why TDD?:

As per IEEE 519, the limit on harmonic current distortion is specified in TDD. Hence, TDD plays key role to compare the harmonic distortion as per IEEE 519.

Best regards,

See Answer In Context

Reply
Replies 5
Anonymous user
Not applicable

Posted: ‎2014-03-25 07:12 AM

0 Likes
0
8037
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-03-25 07:12 AM

I am also interested in this.

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2014-03-25 08:26 AM

1 Like
2
8037
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-03-25 08:26 AM

The PM8 user guide has some information: Page 43 in the PDF, page 37 in the guide.

THD. Total Harmonic Distortion (THD) is a quick measure of the total distortion present in a waveform and is the ratio of harmonic content to the fundamental. It provides a general indication of the “quality” of a waveform. THD is calculated for both voltage and current. The power meter uses the following equation to calculate THD, where H is the harmonic distortion (See guide)

thd. An alternate method for calculating Total Harmonic Distortion, used widely in Europe. It considers the total harmonic current and the total rms content rather than fundamental content in the calculation. The power meter calculates thd for both voltage and current. The power meter uses the following equation to calculate THD, where H is the harmonic distortion: (See guide)

http://download.powerlogic.schneider-electric.com/C12579F100161A32/All/FAF46C3369CDFEB385257A11005B4...

for TDD have a look at http://www.powerlogic.com/kbarticle.cfm?myrequest=RESL205832 for the calculations.

As for the end user benefits I am not sure.

L4 Prime for Advanced metering and Utilities
Reply
Anonymous user
Not applicable

Posted: ‎2014-03-25 09:54 PM

0 Likes
1
8037
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-03-25 09:54 PM

Thanks for the explanation of how to calculate THD, thd & TDD.

I am interested to understand, to End Customer what are the benefit of these 3 measurements.....how do they utilize these values ?

Regards,

Chetan Dhake.

Reply
sesa55514_bridg
sesa55514_bridg Explorer
Explorer

Posted: ‎2014-04-09 12:35 AM

3 Likes
0
8037
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-04-09 12:35 AM

The end-user benefit between THD and thd is really to align with regional expectations (i.e. is it expected to create the ratio based on total RMS or fundamental RMS).

The end-user benefit of TDD is a bit more obvious.  It uses the Demand value to establish a fixed number to use in the ratio calculation.  This creates a more realistic value of the harmful impact of current harmonics, as they are expressed as a ratio against the peak demand rather than whatever the load current happens to be at that moment.  As an example, let's assume there is 250 mA of harmonic content on the 5A nominal CT input of a meter, and the circuit loaded at 2.5A fundamental current.  THD would say the harmonic percentage is 250mA/2.5A, or 10%.  TDD would say the harmonic percentage is 250mA/5A, or 5%.  If the customer is concerned about things like harmonics summing in the neutral, the TDD value gives a better representation of the magnitude of the problem.

Reply
mrsrinivas
mrsrinivas Leader
Leader

Posted: ‎2014-04-24 06:58 AM

1 Like
0
8037
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-04-24 06:58 AM

Hi Chetan,

1) About THD, TDD:

  • TDD                           =     Total Demand Distortion of current.
  • THDI% (or thdi%)      =     Total Harmonic distortion of current.

The reason for above two terminologies as below:

THDI is the ratio of Harmonic current magnitude to Fundamental Current.

  1. i.e. THDI %      =      Ih / I1 x 100.

As the load (or I1)  varies, the ratio (THDI%) will also vary. This makes things complicated to arrive at specific limit of harmonic current. Hence TDD is used as a limiting factor for harmonic current distortion.

TDD             =     Ih / Imax x 100.

Where,

Imax     =     the current at Maximum Demand measured (or calculated) at the Point of Common coupling (PCC).

(PCC can be either Utility metering point or secondary of transformer.)

2) Measurement of THD, TDD:

THDI% can be measured by directly connecting harmonic analyzer or any THD measurable instrument.

But, in most of the situation it may be difficult to measure TDD, as TDD has to be measured at Maximum Demand scenario, hence TDD will be calculated based on THDI% measurement and Maximum Demand data from customer.

3) Why TDD?:

As per IEEE 519, the limit on harmonic current distortion is specified in TDD. Hence, TDD plays key role to compare the harmonic distortion as per IEEE 519.

Best regards,

Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore