PM8243 RSTP communication

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8243 RSTP communication
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
478
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
89
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Anonymous user
Not applicable

Posted: ‎2020-04-29 11:03 AM

0 Likes
2
1404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-04-29 11:03 AM

PM8243 RSTP communication

 

We will have up to 25 power meter (PM8243) in the same loop communicating by RSTP and  IEC 61850 protocol. This is the architecture:

 
 

 

The RSTP root is the Hirschmann switch.

When there is a change in the topology devices have to adjust their settings according to root instructions enabling/disabling their ports. I can see the number of changes in the Hirschmann switch (root) and I can check when the topology is stable (time since topology change) and consulting the MAC addresses connected to each switch port I know where is open the ring.

 

I observed in PM8243 it takes some minutes for the PM8243 device ring to reach the stable RSTP topology after a change, especially when closing the ring. During the process I have ping with all devices but with delays sometimes around hundreds milliseconds and it seems not to lose communications with 61850 master. The recovery times of ping after topology change seem normal : 1s to 10s

 

For example I have measured these times with different PM8243 number in the ring:

  • 6 PM8243 = about 2 minutes to reach RSTP stable
  • 10 PM8243 = about 2 minutes to reach RSTP stable (topology change count=10)
  • 15 PM8243 = about 2 minutes to reach RSTP stable (topology change count=12)
  • 16 PM8243 = about 4 minutes (topology change count=27)
  • 17 PM8243 = about 3 minutes (topology change count=22)
  • 23 PM8343= about 46 minutes

 

I see that from 15 devices it takes longer to reach RSTP stability and it does not always behave the same, even sometimes some PM8243 stays blocked without responding to ping.

 

If we compare the behavior of P3 against PM8243:

  • P3 Relays reach immediately the RSTP stable on the switch, only need 1 count (topology change count=1)
  • PM8243 takes many seconds to reach the stable RSTP topology but never stops responding to ping and takes a few seconds to recover ping after a change.

I have some questions:

  1. Do you know if it is normal for the RSTP ring to take so long to reach stability at startup or after closing the ring?
  2. Do you know if there is a limit of PM8243 in the same loop to work properly RSTP communication?

 

This message is posted on the behalf of:

José Miguel Villegas Altea
Customer Project Engineer
Power Systems Iberia Cluster

 

Labels
  • Labels:
  • PM8000
Tags (2)
  • Tags:
  • @pm8000
  • @RSTP loop
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-04-29 01:09 PM

0 Likes
0
1397
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-04-29 01:09 PM

Waiting to hear back what version of firmware is on the meters being tested.

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-08-05 08:52 AM

1 Like
0
1379
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-08-05 08:52 AM

For anybody looking at this later, V3.0.0 firmware for the PM8000 meter has made a number of improvements. Recommend upgrading the firmware of the meter if you are seeing any RSTP delays.

 

https://www.se.com/ca/en/download/document/PM8000_meter_FW_v003.000.000/
 
https://www.se.com/ca/en/download/document/ION9000_meter_FW_v003.000.000/
https://www.se.com/ca/en/download/document/ION7400_meter_FW_v003.000.000/
 
Regards,
Charles
L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 2
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-04-29 01:09 PM

0 Likes
0
1398
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-04-29 01:09 PM

Waiting to hear back what version of firmware is on the meters being tested.

L4 Prime for Advanced metering and Utilities
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-08-05 08:52 AM

1 Like
0
1380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-08-05 08:52 AM

For anybody looking at this later, V3.0.0 firmware for the PM8000 meter has made a number of improvements. Recommend upgrading the firmware of the meter if you are seeing any RSTP delays.

 

https://www.se.com/ca/en/download/document/PM8000_meter_FW_v003.000.000/
 
https://www.se.com/ca/en/download/document/ION9000_meter_FW_v003.000.000/
https://www.se.com/ca/en/download/document/ION7400_meter_FW_v003.000.000/
 
Regards,
Charles
L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of