Hai
I Have 5 nos of PM8000 MFM connected via Ethernet port ring topology. if i connect one ring end to ethernet switch1 and another end connected to another ethernet switch2. our ESCADA totally loss the communication. so that we keep one one connection. please give me a solution for this. IEC 61850 protocol Is used.
Link copied. Please paste this link to share this article on your social media post.
Hello @sivasara ,
If using the meters in ring topology, need to make sure RSTP is enabled on all meters and network is setup for RSTP. Otherwise meters will be a network loop that can bring down a network fast. IT killing one or both ports is expected.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @sivasara ,
If using the meters in ring topology, need to make sure RSTP is enabled on all meters and network is setup for RSTP. Otherwise meters will be a network loop that can bring down a network fast. IT killing one or both ports is expected.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Good evening Sir/Madam
I am a technician of the company ENERTEAM located in Ivory Coast.
I would like to know if once the PM8000 is installed in a system how to access the information of the PM8000 remotely
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.