PM8000 - TDD output source
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
You can obtain TDD values from the Harmonic Measurement Modules.
For that, you need to:
- Set up the "Display Mode" as "Magnitude Outputs Displayed as Percentages".
- Set up the "THD Display Mode" as "Percentages"
- Link the "Max Demand" input to the source for the peak or maximum demand load current. The demand load current might be a fixed value (provided with an External Numeric Module or Arithmetic Module), or it could be a maximum value over a period of time, calculated with a Sliding Window Demand Module and a Maximum Module.
Under these conditions, the TDD would be the "Total HD" output in your Harmonic Measurement Module.