PM8000 High Speed Metering

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8000 High Speed Metering
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
491
Ramasamy_N
Captain Ramasamy_N Captain
115
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
93
Robert_Lee
Admiral Robert_Lee Admiral
92
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Andy_Hubert
Lieutenant Andy_Hubert Lieutenant
Lieutenant

Posted: ‎2016-09-29 07:55 AM

0 Likes
7
1792
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-09-29 07:55 AM

PM8000 High Speed Metering

I have a customer here who has some PM8000 meters, they would like to read the HS values from the modbus registers shown below.

In Demo mode these do not seem to update any faster than 1 second.

Has anyone tried this before? and do you get a much faster update of the registers.

Thanks

 

HS Current A210002FLOAT32AR/Onumeric---HS I aCT_AMEMNone
HS Current B210022FLOAT32AR/Onumeric---HS I bCT_AMEMNone
HS Current C210042FLOAT32AR/Onumeric---HS I cCT_AMEMNone
HS Current N210062FLOAT32AR/Onumeric---HS I 4CT_AMEMNone
HS Current G210082FLOAT32AR/Onumeric---HS I 5CT_AMEMNone
HS Current Avg210102FLOAT32AR/Onumeric---HS I avgCT_AMEMNone
HS Frequency210162FLOAT32HzR/Onumeric---HS FreqHZMEMNone
HS Voltage, A-B 210182FLOAT32VR/Onumeric---HS Vll abPT_VMEMNone
HS Voltage, B-C 210202FLOAT32VR/Onumeric---HS Vll bcPT_VMEMNone
HS Voltage, C-A 210222FLOAT32VR/Onumeric---HS Vll caPT_VMEMNone
HS Voltage, L-L Average 210242FLOAT32VR/Onumeric---HS Vll avgPT_VMEMNone
HS Voltage, A-N 210262FLOAT32VR/Onumeric---HS Vln aPT_VMEMNone
HS Voltage, B-N 210282FLOAT32VR/Onumeric---HS Vln bPT_VMEMNone
HS Voltage, C-N 210302FLOAT32VR/Onumeric---HS Vln cPT_VMEMNone

HS Voltage, L-N Average

210342FLOAT32VR/Onumeric---HS Vln avgPT_VMEMNone
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
patrickw
Ensign patrickw Ensign
Ensign

Posted: ‎2016-10-04 11:22 AM

2 Likes
1
1692
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-10-04 11:22 AM

Hi Andrew,

You are correct that the HS Power Meter Module only updates once per second in demo mode.  With a non-demo volts mode, the data is refreshed every half-cycle. 

The caveat with reading this over modbus, is that the round-trip comm delay in making a request and getting a response for highspeed data is variable.  Depending on the meter loading it could take up to a second to get a response (metering and logging is always higher priority than comms).  You will need to benchmark it in your specific scenario to see if it will be fast enough for your needs.

See Answer In Context

Reply
Replies 7
Anonymous user
Not applicable

Posted: ‎2016-10-04 07:28 AM

0 Likes
0
1692
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-10-04 07:28 AM

Since the are almost in order I guess it would be smart to create a Modbus Register Group that reads all signals at a time

I assumed it was SmartStruxure, but maybe it wasn´t

Christer

Reply
patrickw
Ensign patrickw Ensign
Ensign

Posted: ‎2016-10-04 11:22 AM

2 Likes
1
1693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-10-04 11:22 AM

Hi Andrew,

You are correct that the HS Power Meter Module only updates once per second in demo mode.  With a non-demo volts mode, the data is refreshed every half-cycle. 

The caveat with reading this over modbus, is that the round-trip comm delay in making a request and getting a response for highspeed data is variable.  Depending on the meter loading it could take up to a second to get a response (metering and logging is always higher priority than comms).  You will need to benchmark it in your specific scenario to see if it will be fast enough for your needs.

Reply
Andy_Hubert
Lieutenant Andy_Hubert Lieutenant
Lieutenant

Posted: ‎2016-10-10 02:15 AM

0 Likes
0
1692
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-10-10 02:15 AM

Hi Patrick,

Thanks for the reply, that is exactly as I had hoped.

My customer is redaing the registers from a PLC connected via TCP, so it should be fast enough.

Thanks

Andy

Reply
DPMalagar
Ensign DPMalagar
Ensign

Posted: ‎2025-01-17 04:42 PM

0 Likes
0
610
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-17 04:42 PM

Hi,

 

I have also same concern with PM8000, but it was monitored to Power Monitoring Expert. Can PM8000 supports the 100ms report template of PME?

Reply
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
Captain

Posted: ‎2025-01-20 04:03 PM

1 Like
1
584
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-20 04:03 PM

Hi @DPMalagar 

 

As mentioned above, communications in ION meters such as PM8000, is the lowest priority on the meter and it is the first thing to get dropped if meter is highly loaded and CPU loading is a factor(meter is busy with power quality events, waveform recordings, alarms, etc.). Therefore there is no way to guarantee high speed communications.

 

For real-time data, PME polls ION meters' data via the native ION protocol within a range of seconds, and the values are updated on the meter's diagram.

 

The 100 ms Report shows 100 ms measurements from the meter where data had been logged before with 100 ms interval on meter's onboard log and is totally different from polling meter and meter's response in 100 ms.


For historical data, depending on the report type and how the meter is configured with the desired interval logs (for example, 15 minutes, 1 minute, 100 milliseconds, etc.), PME retrieves logged data from the meter's onboard log (default is every 30 seconds) and pushes it into the SQL database. Depending on which report is executed, the results are replicated in the report tables.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
DPMalagar
Ensign DPMalagar
Ensign

Posted: ‎2025-01-26 11:09 PM

0 Likes
0
541
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-26 11:09 PM

Hi @Mehran_Mehrnia,

 

Thank you very much for your help. On the PME, does it retrieve the log from the Meter's onboard log even its FIFO? I believe it has a maximum log of 3360, which limits to less than a day, if I used a 1sec interval. I also think that PME has a software log., but I can only edit on 3rd party using Device Type Editor, I cannot locate the default logging file for native PM8000 PME Driver. 

 

Regards,

Dennis

Reply
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
Captain

Posted: ‎2025-01-27 08:31 AM . Last Modified: ‎2025-01-27 08:33 AM

1 Like
0
532
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-27 08:31 AM

Hi @DPMalagar 

 

You're welcome.

Each Data Recorder in the meter for example Load Profile has the log depth(35 days) with 15 minutes interval per each day means 4(each hour has 4*15 minutes)*24(each day is 24 hours)*35 days = 3360 records that each record for example in this Load profile has only 4 linked channels and since the 'Record Mode' is Circular, after 35 days the logged values start to be overwritten as FIFO(first in first out). 

 

The log depth specifies how long the recorder can keep the recorded values before being overwritten and the shorter the logging interval is set, the more log memory is used. As mentioned before, PME retrieves logged data from the meter's onboard log (the default is every 30 seconds), which is sufficient to avoid losing any logged data unless the log depth is too short or the communication between the device and PME is lost for a while, resulting in data being overwritten on the device.

Software logging in PME is only for third-party device drivers, while native devices in PME, such as the PM8000, have their own onboard logging that can be configured directly on the device.

 

If you need more assistance on PME, kindly post your question in the EcoStruxure Power Monitoring Expert forum.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of