【PM8000】Current and voltage measurement accuracy
Metering & Power Quality
  • EcoStruxure Power & Grid
  • 【PM8000】Current and voltage measurement accuracy
Charles_Murison
Picard Charles_Murison Picard
526
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
138
Ramasamy_N
Captain Ramasamy_N Captain
115
Miyai
Lieutenant Miyai
Lieutenant
Posted: ‎2022-08-24 11:55 PM
1984
I would like some advice on how to think about accuracy.
The manual described IEC 61557-12 Class 0.2 for current and voltage.
I checked IEC 61557-12 and confirmed the accuracy is ±0.2%.
What is the “standard value” for this ±0.2%?
My guess is that the reference value is “Imax”.
In the case of PM8000, should Imax be 10A?
Best regards,
Miyai
  • PM8000
DanL
Captain DanL Captain
Captain
Posted: ‎2022-08-25 09:40 AM
1964
Correct. The IEC61557-12 standard requires (Table 22) current measurement uncertainty (for transformer connected circuits) to be specified as a percent of reading over the range from 10% In (10% of 5A = 50mA) to Imax (10A).
Charles_Murison
Posted: ‎2022-08-25 09:20 AM
2
1968
Hello @Miyai
When the accuracy is ±0.2%, this is relative to the measurement itself. If you input was 1.250 A, the meter would measure between 1.2525 A and 1.2475.  If input was 2.500A, the meter would measure between 2.505 A and 2.495 A.
Charles
DanL
Captain
1965
Miyai
Lieutenant Miyai
Lieutenant
Posted: ‎2022-08-25 05:36 PM
Hello @DanL , @Charles_Murison
Thank you  for the advice.
I will check the IEC standard again.
Best regards,
Miyai