Hello,
I would like some advice on how to think about accuracy.
The manual described IEC 61557-12 Class 0.2 for current and voltage.
I checked IEC 61557-12 and confirmed the accuracy is ±0.2%.
What is the “standard value” for this ±0.2%?
My guess is that the reference value is “Imax”.
In the case of PM8000, should Imax be 10A?
Best regards,
Miyai
Link copied. Please paste this link to share this article on your social media post.
Correct. The IEC61557-12 standard requires (Table 22) current measurement uncertainty (for transformer connected circuits) to be specified as a percent of reading over the range from 10% In (10% of 5A = 50mA) to Imax (10A).
Link copied. Please paste this link to share this article on your social media post.
Hello @Miyai
When the accuracy is ±0.2%, this is relative to the measurement itself. If you input was 1.250 A, the meter would measure between 1.2525 A and 1.2475. If input was 2.500A, the meter would measure between 2.505 A and 2.495 A.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Correct. The IEC61557-12 standard requires (Table 22) current measurement uncertainty (for transformer connected circuits) to be specified as a percent of reading over the range from 10% In (10% of 5A = 50mA) to Imax (10A).
Link copied. Please paste this link to share this article on your social media post.
Hello @DanL , @Charles_Murison
Thank you for the advice.
I will check the IEC standard again.
Best regards,
Miyai