Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PM5563: Meter Question on System Type

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM5563: Meter Question on System Type
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
khkao
khkao Leader
Leader

Posted: ‎2022-05-18 01:08 PM . Last Modified: ‎2022-05-18 01:33 PM

0 Likes
2
4735
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-05-18 01:08 PM

PM5563: Meter Question on System Type

Hey all,

 

Recently, at a MSFT Datacenter project, we have been met with the issue of determining the correct meter system type for the connection provided by the LV Switchgear vendor. It is physically wired up as a 3Ph3W open delta 2PT/3CT connection, but the meter itself does not have an option for a 3P3W Open Delta. There are a total of 5 options available for a 3Ph3W connection:

  1. 3Ph3W Delta Ungrounded
  2. 3Ph3W Delta Corner Grounded
  3. 3Ph3W Wye Ungrounded
  4. 3Ph3W Wye Gnd
  5. 3Ph3W Res Gnd

For background, I've included 3 files. One of the equipment meter drawings, one of the PM5563 Installation guide, and one of the record drawings for the site. The record drawings show that the Primary MV XFMR secondary is tapped as a Wye with HRG. The wiring in the equipment drawings almost match one of the example wiring configurations for the meter in the installation guide, with the exception of the meter pulling a neutral off V2 in the equipment drawings. 

My question to the team is: What is the best practice meter system type for the PM5563 that is shown in the equipment drawings attached? The customer would like to know the thought process and system type that the team had when putting together the installation guide and the example wiring shown that reflects that of the wiring on site. Thank you, and I appreciate any advice on the matter.

Attachments
Labels
  • Labels:
  • PM5000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2022-05-20 05:07 AM

0 Likes
0
4647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-05-20 05:07 AM

Hello @khkao 

 

You can select 3PH3W Delta Corner Grounded system type in PM5563 meter 3Ph3W open delta 2PT/3CT connection which is generally followed for such equipment. 

The connection diagram for this system type to be followed as below, 

 

 

Capture.JPG

There is mistake in the installation diagram (V2 and VN shorted in meter terminal) which will be corrected. 

 

Regards, 

Ramasamy N

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 2
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2022-05-19 08:23 AM

0 Likes
0
4691
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-05-19 08:23 AM

Hello @Ramasamy_N,

 

Are you able to answer this question?

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2022-05-20 05:07 AM

0 Likes
0
4647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-05-20 05:07 AM

Hello @khkao 

 

You can select 3PH3W Delta Corner Grounded system type in PM5563 meter 3Ph3W open delta 2PT/3CT connection which is generally followed for such equipment. 

The connection diagram for this system type to be followed as below, 

 

 

Capture.JPG

There is mistake in the installation diagram (V2 and VN shorted in meter terminal) which will be corrected. 

 

Regards, 

Ramasamy N

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore