Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PM5560 meter swap

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM5560 meter swap
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
566
Mehran_Mehrnia
Mehran_Mehrnia Champion
194
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
danielbarrantes
danielbarrantes
Troubleshooter

Posted: ‎2024-02-22 07:06 AM

0 Likes
3
2633
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-02-22 07:06 AM

PM5560 meter swap

Hello, currently a client has a PM5560 meter with a completely blank screen, however the meter does communicate to the PME. This meter is going to be replaced by another PM5560 and I would like to know what is the best or most transparent way to make this change so that, for example, the energy count can continue on the new meter, starting from where it left off on the old one PM5560.

 

Is this possible ? Is it possible to change the meter of the same model and for PME to practically "not feel the change"?.

 

Thanks. @Charles_Murison @Ricardo_RM 

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2024-02-26 08:06 AM . Last Modified: ‎2024-02-26 08:07 AM

1 Like
0
2568
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-02-26 08:06 AM

Hello @danielbarrantes 

Yes, you can enter the present meter energy values in the new meter using "preset energy" option in ION setup. 

Please note this preset energy feature in not done in ION setup for PM5560, you need to change the template option as "PM5340 v2013" and enter energy values manually. 

Refer the screenshots for more details. 

 

Also raise the TEX case for further analysis of blank screen meter. 

 

Regards, 

 

See Answer In Context

Attachments
Reply
Replies 3
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2024-02-22 08:54 AM

0 Likes
0
2629
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-02-22 08:54 AM

Hello @danielbarrantes ,

 

In PME, a like for like meter replacement should not have any trouble.

 

Sorry I do not know all the capabilities of the PM5000 series of meters. I have moved your post to the hardware forum as this is more meter specific than PME specific. I hope others in the forum can answer this question.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
ryanmathes
ryanmathes Explorer
Explorer

Posted: ‎2024-02-22 01:19 PM . Last Modified: ‎2024-02-23 08:02 AM

1 Like
0
2618
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-02-22 01:19 PM

Hello @danielbarrantes ,  I see from the modbus register map for the PM5560 there is a command for "Preset Accumulated Energy". 

 

I have not done this process myself but it looks like it would be possible via these modbus commands. 

 

ryanmathes_0-1708636627641.png


FAQ to modbus map 
https://www.se.com/us/en/faqs/FA234017/

 

This FAQ has more information on the meter's Semaphore which may be helpful as well.
https://www.se.com/us/en/faqs/FA241856/

 

Thanks,

 

Ryan Mathes

Reply
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2024-02-26 08:06 AM . Last Modified: ‎2024-02-26 08:07 AM

1 Like
0
2569
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-02-26 08:06 AM

Hello @danielbarrantes 

Yes, you can enter the present meter energy values in the new meter using "preset energy" option in ION setup. 

Please note this preset energy feature in not done in ION setup for PM5560, you need to change the template option as "PM5340 v2013" and enter energy values manually. 

Refer the screenshots for more details. 

 

Also raise the TEX case for further analysis of blank screen meter. 

 

Regards, 

 

Attachments
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore