Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PM5560 Polarity

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Re: PM5560 Polarity
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
577
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
arjanbijker
arjanbijker Leader
Leader

Posted: ‎2015-02-03 04:51 AM

0 Likes
9
3886
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-02-03 04:51 AM

PM5560 Polarity

Hi,

With the PM800 you could change current polarity settings via modbus commands.

Can the PM5560 do the same?

We have a whole bunch of them installed in datacenters where it is not possible to shutdown power that easily.

Tags (1)
  • Tags:
  • polarity
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Usha
Usha Mentor
Mentor

Posted: ‎2015-02-11 02:13 AM

0 Likes
0
3680
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-02-11 02:13 AM

Hi Victor,

Discussed with L4 product prime regarding modbus commands to change current polarity in PM5560. Thanks for above screenshot with register details. I will discuss again and will get back to you with the latest updates.


Regards,
Usha
Software Engineering Support

See Answer In Context

Reply
Replies 9
VictorMarincus
VictorMarincus Champion
Champion

Posted: ‎2015-02-03 06:13 AM

0 Likes
0
3681
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-02-03 06:13 AM

That is a very good question, Arjan.

The PM556x_ModbusRegisterList shows the needed registers (ref. to "Logical Phase" ...) similar to PM800 series, however the command sequence is different.

Perhaps , can help.

Reply
sesa294402
sesa294402 Leader
Leader

Posted: ‎2015-02-04 01:09 AM

0 Likes
2
3681
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-02-04 01:09 AM

Hi Arjan,

Can you explain how to change CT polarity with Modbus command? What type of meters that we can do that?

Thanks & Best regards,

Tran Bao Duong

Reply
arjanbijker
arjanbijker Leader
Leader

Posted: ‎2015-02-04 01:32 AM

1 Like
1
3681
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-02-04 01:32 AM

RESL210828

http://www.powerlogic.com/kbarticle.cfm?myrequest=RESL210828

Reply
sesa294402
sesa294402 Leader
Leader

Posted: ‎2015-02-04 01:37 AM

0 Likes
0
3681
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-02-04 01:37 AM

Sorry but I don't see any document with RESL210828. Maybe I'm not authorized to access this link.

Reply
Usha
Usha Mentor
Mentor

Posted: ‎2015-02-11 12:35 AM

0 Likes
4
3681
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-02-11 12:35 AM

Unfortunately, you can not change the current polarity through modbus commands in PM5560.


Regards,
Usha
Software Engineering Support
Reply
VictorMarincus
VictorMarincus Champion
Champion

Posted: ‎2015-02-11 01:31 AM

1 Like
3
3681
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-02-11 01:31 AM

So there's no way to do that? I am surprised.

Then the register list for PM556x is inconsistent.

Why a conditional write is mentioned then on the "[DEAD LINK /message/12539#12539]PM556x_ModbusRegisterList_V1.0.02-Public version.xlsx"?

5714

Reply
Usha
Usha Mentor
Mentor

Posted: ‎2015-02-11 02:13 AM

0 Likes
0
3681
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-02-11 02:13 AM

Hi Victor,

Discussed with L4 product prime regarding modbus commands to change current polarity in PM5560. Thanks for above screenshot with register details. I will discuss again and will get back to you with the latest updates.


Regards,
Usha
Software Engineering Support
Reply
Anonymous user
Not applicable

Posted: ‎2015-02-11 08:18 AM

0 Likes
0
3681
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-02-11 08:18 AM

Thanks for pointing those out Victor.  I missed them on my pass through the register list.

Brian

Reply
Usha
Usha Mentor
Mentor

Posted: ‎2015-02-18 12:54 AM

2 Likes
0
3681
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-02-18 12:54 AM

Hi Victor,

These registers are not configurable.


Regards,
Usha
Software Engineering Support
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore