Hello,
I hope you all are well.
I have a PM5563 din rail mounted energy analyzer with 02.04.02 firmware.
1. I connected PM5563 from my laptop via ethernet
2. I used Web (chrome browser) with default IP 169.254.0.10
3. I changed the IP as 192.168.1.10
after that, I cannot reach the EA.
I think I need to update firmware but how? I can't even reach it
do you have an idea to solve this problem?
thank you
Link copied. Please paste this link to share this article on your social media post.
Hello @Anonymous user ,
When you changed the IP address of the meter, did you change the IP address of you laptop to be in the same subnet? This is a combination of the IP address and subnet mask settings.
Eg IP address 192.168.1.10 with subnet mask 255.255.255.0, would require your laptop IP address is 192.168.1.xxx to be able to talk to the meter.