PM5310 integration in DCS systemEmerson DeltaV - problem with FLOAT32 registers

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM5310 integration in DCS systemEmerson DeltaV - problem with FLOAT32 registers
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Anonymous user
Not applicable

Posted: ‎2019-11-06 05:08 AM . Last Modified: ‎2019-11-06 05:23 AM

0 Likes
2
1249
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-11-06 05:08 AM

PM5310 integration in DCS systemEmerson DeltaV - problem with FLOAT32 registers

Hello everyone,

 

I have a customer who has PM5310 connected to DCS system Emerson Delta V via Modbus RS485. He wants to read basic data like current, voltage and power. He reads them from the bellow registers, but the values he sees in the software are very different from the ones on the display. I think the problem is with the Float32, because we tried to read the CT Primary and Secondary, which are INT16U and the data was correct. Here are the registers he would like to read:

 

1 - Currents 3000-3004 FLOAT32

2 - Voltages 3020-3024 FLOAT 32

3 - Power 3060, 3068, 3076 FLOAT32 

 

Any idea what could be the problem?

 

Thanks and Regards,

Mariya

 

Attachments
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2019-11-06 09:12 AM

2 Likes
1
1242
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-11-06 09:12 AM

If the DCS system is unable to properly interpret FLOAT32 values, the PM5xxx devices have no other registers available which only support 16 bit registers for meter readings (certain settings are defined as 16 bit when resolution isn't required).  There are obvious reasons why the firmware developers pick FLOAT32 for readings where users want to both be able to see both register resolution AND have large display ranges (ex. GW down to milliWatts) which FLOAT32 registers provide.

 

My guess is that the DCS system is attempting to read the FLOAT32 registers as 16 bit Modbus ones and showing those values which would be incorrect.  The customer needs to see if the DCS system is capable of reading FLOAT32 values instead.

See Answer In Context

Reply
Ramasamy_N
Captain Ramasamy_N Captain
Captain

Posted: ‎2019-11-08 05:03 AM

1 Like
0
1238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-11-08 05:03 AM

You can suggest to read 2 registers in UINT16 format and convert it to FLOAT32 as per IEEE-754 converter.

 

See Answer In Context

Reply
Replies 2
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2019-11-06 09:12 AM

2 Likes
1
1243
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-11-06 09:12 AM

If the DCS system is unable to properly interpret FLOAT32 values, the PM5xxx devices have no other registers available which only support 16 bit registers for meter readings (certain settings are defined as 16 bit when resolution isn't required).  There are obvious reasons why the firmware developers pick FLOAT32 for readings where users want to both be able to see both register resolution AND have large display ranges (ex. GW down to milliWatts) which FLOAT32 registers provide.

 

My guess is that the DCS system is attempting to read the FLOAT32 registers as 16 bit Modbus ones and showing those values which would be incorrect.  The customer needs to see if the DCS system is capable of reading FLOAT32 values instead.

Reply
Ramasamy_N
Captain Ramasamy_N Captain
Captain

Posted: ‎2019-11-08 05:03 AM

1 Like
0
1239
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-11-08 05:03 AM

You can suggest to read 2 registers in UINT16 format and convert it to FLOAT32 as per IEEE-754 converter.

 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of