PM5110 Pulsed Output Pulse Period (Seconds) - Issue

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM5110 Pulsed Output Pulse Period (Seconds) - Issue
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
casey_skillen_s
casey_skillen_s Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2015-10-05 06:46 AM

0 Likes
4
1469
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-10-05 06:46 AM

PM5110 Pulsed Output Pulse Period (Seconds) - Issue

Good afternoon guys

Does anybody know how to calculate the pulse period on the digital output terminal of the above meter?

In the user guide i can see 25Hz is the maximum pulse frequency so does this mean 1/25 or 0.04 seconds is the pulse period ?

I am having an issue where we have tried 3 meters connected to a BMS and we have configured the meter as follows

Pulse Mode - Energy

Channel - Active Del

Pulse - 1Pulse/kWh

LED is set to the following

Pulse Mode - Energy

Channel - Active Del

Pulse - 1Pulse/kWh

The digital output has  volts input from the BMS but we are seeing no output

Is there anything you could advise that i am doing wrong?

Regards

Casey

Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Usha
Lt. Commander Usha Lt. Commander
Lt. Commander

Posted: ‎2015-10-06 02:57 AM

0 Likes
0
1403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-10-06 02:57 AM

Hi Casey,

Please raise a ticket to technical support.


Regards,
Usha
Software Engineering Support
Reply
Simon_C
Admiral Simon_C Admiral
Admiral

Posted: ‎2015-10-06 01:02 PM

0 Likes
0
1403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-10-06 01:02 PM

I have had a similar problem after swapping out a PM700P for a PM5110.

All I could get from technical support was that it must be a short pulse (by my calcs, 25Hz at 50% duty is 20 ms on and 20 ms off).

The PM700P allowed the pulse length to be programmed from a choice of values including 300 ms, which is long enough to see on a multimeter display when testing, and also be detected by most types of BMS input.

The PM5110 does not seem to have this feature, AND does not allow programming for say 1 pulse per 10 kWh, only 1 or more pulses per 1 kWh.

I know most new meters are connected using modbus, but we really need a new model of meter that can be used to directly replace a faulty old model with the same pulse count functionality.

Outputs

Digital output

Max load voltage 40 V DC

Max load current 20 mA

On Resistance 50 Ω max

Meter constant

from 1 to 9,999,999 pulses per k_h (k_h = kWh,

kVARh or kVAh depending on the energy parameter

selected)

Pulse width for Digital Output 50% duty cycle

Pulse frequency for Digital Output 25 Hz max.

Leakage current 0.03 micro Amps

Isolation 5 kV rms

Optical outputs

Pulse width (LED) 200 s

Pulse frequency 50 Hz. max.

Meter constant from 1 to 9,999,999 pulses per k_h

Reply
Simon_C
Admiral Simon_C Admiral
Admiral

Posted: ‎2015-10-23 03:40 AM

0 Likes
0
1404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-10-23 03:40 AM

Is there an update from technical support on this?

We have hundreds of PM700P and PM750 meters installed with just a pulse output to a BMS controller, and some of them get damaged or fail so need replacing.

As reported above, the PM5110 has been tried but has a very short pulse length so does not suit all BMS pulse count inputs.

My research on the PM53xx range has found parameters to change the pulse length on the digital outputs, but the outputs cannot be configured for Energy only Alarms.

Does anyone know of a new model of meter (panel facia mounted) that can provide a pulse output of at least 300 ms for energy consumption?

If not, can the firmware in the PM5110 be updated to allow adjustment of the pulse length as was included on the older PM700P and PM750 meters?

Reply
juaotor
Lieutenant juaotor Lieutenant
Lieutenant

Posted: ‎2015-11-06 12:38 AM

0 Likes
0
1404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-11-06 12:38 AM

Hello,

please raise your question to: gb-customerservices@schneider-electric.com

Thank you!

JM

JMO
Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of