Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PM5000 depth vs PM700 depth - what can cover the difference

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM5000 depth vs PM700 depth - what can cover the difference
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
566
Mehran_Mehrnia
Mehran_Mehrnia Champion
194
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
Start a Topic
sesa233557
sesa233557 Leader
Leader

Posted: ‎2015-05-04 05:35 AM

0 Likes
3
1294
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-05-04 05:35 AM

PM5000 depth vs PM700 depth - what can cover the difference

Hello everyone,

more and more customers are asking for the reason why there is greater depth of the PM5000 than PM700 meters. PM700 is 50mm deep but PM5000 depth is at least 72mm!

This is the real issue when it comes to mounting in Prisma. I've got answer from Prisma product manager, that in that case, PM5000 should be mounted in cable duct. But usually, it's not best fit solution or even not possible solution.

I can't find any mounting kit, but there is need for some kind of pad, that would make PM5000 depth-compatible to PM700.

Have you got any suggestion for solving this problem?

In my case, that can break the sales, unless this problem is solved. And now, at this very week, the customer needs Schneider solution or product to cover this incompatibility.

So I'll be very grateful for prompt help or any help as well.

BR,

Janusz

Tags (2)
  • Tags:
  • pm5000
  • pm700
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
sesa233557
sesa233557 Leader
Leader

Posted: ‎2015-06-10 06:35 AM

0 Likes
1
1228
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-06-10 06:35 AM

Hello everyone, I would like to refresh the topic:

has anybody problem with the depth of the PM5000s, which is 72mm and it is grater than PM700 depth?

It is serious problem when it comes to mounting it in Prisma as well as in other switchboards. Have you got any clue to work this out?

BR,

JM

Reply
Sam_Gaib
Sam_Gaib Troubleshooter
Troubleshooter

Posted: ‎2015-06-19 02:20 PM

0 Likes
0
1229
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-06-19 02:20 PM

Hi Janusz: Do you know if a PM5000 is necessary?  Perhaps a PM3000 could be used instead?

: do you have any suggestions?

Reply
Daniel_Brandao
Daniel_Brandao Mentor
Mentor

Posted: ‎2015-06-20 03:35 AM

0 Likes
0
1229
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-06-20 03:35 AM

Hi . I am aware of the topic and it's a problem in other countries as well. We don't have a solution for it yet, but I am looking into an adapter kit for PM5000 and Prisma panels. It will take us some time to come up with it, but I will keep you posted. The other option is to use the remote display, but that would only work for PM55xx. Again, I will work with the team to try to figure out the best way to solve this. In the meantime, can you send me example pics so I am sure we are really talking about the same problem, same panel? Thanks!

Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore