Do we need to remove all inputs from PM series meters (such as Voltage & Current Inputs) while doing a firmware upgradation? I will very thankful for any guidance in this matter. 🙂
Link copied. Please paste this link to share this article on your social media post.
Hello @Asif_Khan ,
No the voltage and current connections do not have to be removed to upgrade a meter. I would recommend disconnecting any software that may be trying to talk to the meter.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @Asif_Khan ,
No the voltage and current connections do not have to be removed to upgrade a meter. I would recommend disconnecting any software that may be trying to talk to the meter.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hi @Asif_Khan
Also, if meter has any IO connections like Digital output, their state during a firmware upgrade may change.
Best Regards,
-Mehran