Dear Members, we apologize for any disruption or inconvenience caused by the recent spam incidents, and we want to assure you that our dedicated team is actively investigating each reported instance of spam and implementing robust measures to mitigate the impact. Learn more on Spams Mitigation Guidelines
Thank you,
Schneider Electric Community Team
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Link copied. Please paste this link to share this article on your social media post.
Hello Community,
I have a question regarding METSEPM2KANLGIO22, is posible to configure one of the analog inputs as 4-20 mA input and the another input as 12 .. 30 V input?
Thanks for your help, ...
Link copied. Please paste this link to share this article on your social media post.
we have only one option for setting analog output i.e to use current (4-20 ma) for this module.
PM2000 analog IO module can support only with 4-20mA current ranges for both input and output channels and it does not support for voltage based IO's