Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84435members
353634posts

PM1200 Block or individual pamameter question

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

skkim_isama_net
Lieutenant | EcoXpert Master Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master
0 Likes
1
254

PM1200 Block or individual pamameter question

Hellow schneider H/W Team!!

This quesion related PM1200 meter modbus communication.

PM1200 communication seperates individual or block communication method

Unfortunately, there is not enough explanation in my case.

In my question.

both of the block and individual provide RMS value?

why is it seperates two kind of type?

what is best choose the parameter scada system?

please warmly tell the my question

thank you and have a nice day

Attachments
1 Reply 1
Ramasamy_N
Commander Commander
Commander
0 Likes
0
221

Re: PM1200 Block or individual pamameter question

Hi Kim Seong-geun,

Please see my replies in Green.

both of the block and individual provide RMS value? Yes. You can read.

why is it separates two kind of type?Block read is general read and Individual read is requirement form SCADA system to minimise the number of poll.

what is best choose the parameter scada system? -  For basic parameters individual read will be the best suitable for SCADA system.