I need the modbus table to read the PM1000H LCD power meter values such as voltages, current, power factor, ...etc
Link copied. Please paste this link to share this article on your social media post.
Hello @yazeed_eastjo_c ,
If you are referring to the EasyLogicTM PM1000 Series Power Meter, please refer to the user guide, https://www.se.com/ww/en/download/document/NHA1696401/
In this guide the PM1200 meter supports Modbus RTU, the PM1000 does not. (page 13)
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Go with following Link to get Modbus Address
Link copied. Please paste this link to share this article on your social media post.
Hello @yazeed_eastjo_c ,
If you are referring to the EasyLogicTM PM1000 Series Power Meter, please refer to the user guide, https://www.se.com/ww/en/download/document/NHA1696401/
In this guide the PM1200 meter supports Modbus RTU, the PM1000 does not. (page 13)
Regards,
Charles