PM1000H Current Reading Mismatch

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM1000H Current Reading Mismatch
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
491
Ramasamy_N
Captain Ramasamy_N Captain
115
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
93
Robert_Lee
Admiral Robert_Lee Admiral
92
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
ciklee
ciklee
Cadet

Posted: ‎2023-11-16 08:09 PM

0 Likes
5
2722
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-16 08:09 PM

PM1000H Current Reading Mismatch

Hello,

We have a digital power meter EasyLogic PM1000H that we're trying to read the average voltage and current readings via Modbus RTU. However, we're getting mismatched current readings e.g. the LCD shows current readings of ~300A but the Modbus read shows ~1A. The voltage readings are good though e.g. both show ~245V.

Does anyone know what could be the problem? The Modbus register address that we read the average current from is 3010.

Thanks. 

Labels
  • Labels:
  • Power Quality
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2023-11-23 10:23 AM

0 Likes
0
2601
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-23 10:23 AM

If you have access to ION Setup, you can use the Modbus Tester UI (highlight the meter, go to Tools -> Diagnostics and click on the Troubleshooting tab).  From the drop list, you can select Read Holding Register (0x03) enter the register address (3000) and the number of registers to read (12) and click Send.  Once data is returned, right click on any value and select Float 32B as the desired format.

Robert_Lee_0-1700763786472.png

 




See Answer In Context

Reply
Replies 5
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2023-11-17 10:06 AM

0 Likes
0
2705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-17 10:06 AM

Hello @ciklee ,

 

I am not PM1000 series expert so understand what I say could be wrong. The PM1000 series user guide suggests that only the PM1200 meter supports modbus https://www.se.com/ca/en/download/document/NHA1696401/ (page 13). It could be there have been changes made since this guide, new products or you have PM1200 meter. 

 

Using the above guide as reference I would question what registers you are using. Below is for individual readings.

Charles_Murison_0-1700239701581.png

The below set of registers need to be read as a block, all 20 registers at the same time.

Charles_Murison_1-1700242538420.png

 

Do you have examples of the raw data compared to what you except? Ideally per register rather than having registers grouped. 


Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
ciklee
ciklee
Cadet

Posted: ‎2023-11-18 08:17 PM

0 Likes
0
2638
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-18 08:17 PM

Hi @Charles_Murison,

 

Our actual DPM model is PM1125H, which belongs to the EasyLogic PM1000H series (see photo below). Attached are the datasheet and Modbus register list in Excel file for this model.

PM1000H.png 

 

The average voltage and current register addresses are 3036 and 3010, respectively according to the Excel file (screenshot below). Example raw data we're getting when reading these registers are 1131580239 for voltage and 1064509323 for current. When converted using IEEE754 calculator (e.g. https://www.omnicalculator.com/other/floating-point), the floating point values are 242.54V for voltage and 0.95A for current. The voltage reading is similar to those shown on the LED display of the DPM, but the current value is way off. The current shown on the LED display is in the range of 300++A (see screenshot above) but the value read from Modbus register is only ~1A.

ciklee_0-1700367227089.png

 

Appreciate any help. Thanks.

Attachments
Reply
KPS
KPS
Cadet

Posted: ‎2023-11-19 03:14 PM

0 Likes
1
2640
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-19 03:14 PM

Hello @Charles_Murison 

 

PM1000H (Hexa) series does have Modbus connection:

https://www.se.com/in/en/download/document/PLSED310089EN_Web/

 

and the Modbus register for current does match:

https://www.se.com/in/en/faqs/FA333460/

 

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2023-11-20 12:12 PM . Last Modified: ‎2023-11-20 02:02 PM

0 Likes
0
2622
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-20 12:12 PM

Hello @cikleeand @KPS  ,

 

Thank you for the links. I am not PM1000 series expert so I did not know about these links. Are you able to give the values for registers 3000 -> 3012, with each register on it's own? Yes 3011 and 3012 are not currents but request is intentional.

For example
3000: XXXX

3001: YYYY
....
3012: ZZZZ 

Just as a note, I was not able to see your images in previous post.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2023-11-23 10:23 AM

0 Likes
0
2602
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-23 10:23 AM

If you have access to ION Setup, you can use the Modbus Tester UI (highlight the meter, go to Tools -> Diagnostics and click on the Troubleshooting tab).  From the drop list, you can select Read Holding Register (0x03) enter the register address (3000) and the number of registers to read (12) and click Send.  Once data is returned, right click on any value and select Float 32B as the desired format.

Robert_Lee_0-1700763786472.png

 




Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of