Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84394members
353583posts

PM 820 Harmonics

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

aaron_azzo_com_
Ensign
Ensign
0 Likes
2
263

PM 820 Harmonics

Good afternoon all.

Upon looking at some values from one of our Portable PM820's that just came back from a client's site, I noticed some erroneous current THD readings:

5492

I'm aware that anything below 1 ampere will have a multiplying affect on harmonics, but this is not the case here.  Also, please note how the values (current) before and after the boxed value are very similar, and yet the % of THD is almost 40% different.  Any explanations on how this could be above 100% would be fantastic.

Tags (3)
2 Replies 2
JamesAZZO
Sisko | EcoXpert Master Sisko | EcoXpert Master
Sisko | EcoXpert Master
0 Likes
0
204

Re: PM 820 Harmonics

How can THD ever really be over 100%?

sesa44646
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
0
204

Re: PM 820 Harmonics

, can you direct this to the right person?