PCS+'s Capacitor Bank CTs purpose and accuracy

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PCS+'s Capacitor Bank CTs purpose and accuracy
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Mannguyen
Lieutenant | EcoXpert Master Mannguyen Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2024-11-25 10:00 PM

0 Likes
6
823
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-25 10:00 PM

PCS+'s Capacitor Bank CTs purpose and accuracy

Hi All,

Please advise me on the questions from many customers when we offer the Active Harmonic Filter PCS+:

- What is the purpose of the CTs installed in the Cap. Bank Bus? Is it an option or mandatory?

- A new customer who we offer to, as the attached picture. The question on the SLD of CTs connection is: What is the accuracy of current detection since the discrepancy of CT's amp. rate and Cap. Bank bus Breaker's amp. rate (5000A vs 2500A rates)?  

I appreciate it if you kindly share the SE documents that have clarified the above-mentioned questions.

Thank you all in advance

Attachments
Labels
  • Labels:
  • Power Quality
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Yan_Zhang
Ensign Yan_Zhang Ensign
Ensign

Posted: ‎2024-11-28 05:06 PM

1 Like
5
758
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-28 05:06 PM

Hello Mannguyen,
The purpose of the CTs installed in the Cap is to avoid resonance and potential high current damage Cap, improve PCSP's performance. Because Cap shows low impedance for harmonics and amplify harmonics. Measured source current by PCSP must subtract the current of Cap at load side, so the net of the CT signal does not include the CTs current.

Yan_Zhang_0-1732842168379.png

 

The parameters of CTs(source, CAP) must keep align, for specific requirements, please refer installation guide(attached) an consult with local standard.

Yan_Zhang_1-1732842318781.png

BRs

See Answer In Context

Attachments
Reply
Replies 6
Yan_Zhang
Ensign Yan_Zhang Ensign
Ensign

Posted: ‎2024-11-28 05:06 PM

1 Like
5
759
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-28 05:06 PM

Hello Mannguyen,
The purpose of the CTs installed in the Cap is to avoid resonance and potential high current damage Cap, improve PCSP's performance. Because Cap shows low impedance for harmonics and amplify harmonics. Measured source current by PCSP must subtract the current of Cap at load side, so the net of the CT signal does not include the CTs current.

Yan_Zhang_0-1732842168379.png

 

The parameters of CTs(source, CAP) must keep align, for specific requirements, please refer installation guide(attached) an consult with local standard.

Yan_Zhang_1-1732842318781.png

BRs

Attachments
Reply
Mannguyen
Lieutenant | EcoXpert Master Mannguyen Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2024-12-01 03:00 AM

0 Likes
4
719
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-01 03:00 AM

Thank you, @Yan_Zhang for your answer. I've carefully reviewed the NHA41798-2.pdf document and other relevant SE official documents, but I haven't found any specific information regarding the connection of Cap. bank bus' CTs for the PCS+.

I understand that we received this information during training courses, but unfortunately, our customers require an official SE document to approve the Technical Proposal we submitted for the PCS+ offers.

I would be grateful if you could clarify whether there is an official SE document that addresses the Cap. bank bus' current transformers installed for the PCS+. Thank you once again.

 

Reply
caimin_pan
Ensign caimin_pan Ensign
Ensign

Posted: ‎2024-12-01 10:37 PM

1 Like
3
691
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-01 10:37 PM

Download from  DP & DS Offers & Launch - CT 2 Masters & 1 PFC downstream.dwg - All Documents FYI

caimin_pan_1-1733121408859.png

 

Reply
Mannguyen
Lieutenant | EcoXpert Master Mannguyen Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2024-12-02 08:19 PM

0 Likes
2
669
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-02 08:19 PM

I could not access this link: 

Mannguyen_0-1733199394166.png

I would appreciate your help sending the document in the attached file. Thank you in advance.

Reply
caimin_pan
Ensign caimin_pan Ensign
Ensign

Posted: ‎2024-12-02 09:13 PM

1 Like
1
661
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-02 09:13 PM

FYI

Attachments
CT 2 Masters & 1 PFC downstream.dwg
Reply
Mannguyen
Lieutenant | EcoXpert Master Mannguyen Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2024-12-03 08:14 PM

0 Likes
0
636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-03 08:14 PM

Thank you, @caimin_pan. I also recently received this CTs connection diagram from the local FSSE staff when he submitted it to our customer. Unfortunately, our customers require an official SE document like an Installation Manual or CT connection Guideline... for PCS+ with Cap. bank bus CT related... to approve the Technical Proposal we submitted for the PCS+ offers.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of