Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PCS plus with issue: Control Board Initialization Progress

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PCS plus with issue: Control Board Initialization Progress
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
566
Mehran_Mehrnia
Mehran_Mehrnia Champion
194
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Related Products
product field
PowerLogic
AccuSine PCS+

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
tien_dat
tien_dat Explorer
Explorer

Posted: ‎2023-05-08 09:13 AM

0 Likes
3
3771
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-08 09:13 AM

PCS plus with issue: Control Board Initialization Progress

Hello Communities,

I met the issue with PCS Plus during commissioning as below "Control Board Initialization Progress…” Could you help me with this case?

 

Thank you

 

  • Thumbnail of AccuSine PCS+
    PowerLogic
    AccuSine PCS+
View products (1)
Attachments
Labels
  • Labels:
  • Power Quality
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Arunprasad
Arunprasad Mentor
Mentor

Posted: ‎2023-05-09 11:36 AM

1 Like
2
3736
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-09 11:36 AM

Hello Tien Dat

"Control Board Initialization Progress…” means, it is try to reboot by itself , this kind of symptoms are observed when the unit in Turned on with the input supply, but important thing is it get disappears after sometime, so what i want to understand is, did this symptom was continuously displaying on the screen.

If the answer is Yes, then it is due to some event happened in the unit.

From the image shared, i could see Red Flag was pop-up in the HMI, it clearly determines that there could be some event in the unit.

Can you capture the fault event by pressing the Red flag,  i mean when you press the Red flag, it will take you to the next screen , where you can see the fault event . Please capture a small video or an similar kind of image and share it with us.

In addition, i recommend to download the Event log file from the HMI .

Event Log screen displays events that occurred.

Touch an event to select it.

Press the magnifying glass icon  to display the details for that event.

You can save the Event Log to a USB storage device.

Once it is connected, press this icon to save the file.

In addition to that, please collect the commercial reference , unit serial number and is the unit is standalone or connected in parallel.

Note: After collecting all the detail, i recommend you to raise a BFO case through your country "CCC" team, Customer Care Center. Here below attached the link in both English and Vietnamese

English

https://www.se.com/vn/en/work/support/customer-care/contact-schneider-electric.jsp

 

Vietnamese

https://www.se.com/vn/vi/work/support/customer-care/contact-schneider-electric.jsp

 

Regards

Arunprasad

See Answer In Context

Reply
Replies 3
Arunprasad
Arunprasad Mentor
Mentor

Posted: ‎2023-05-09 11:36 AM

1 Like
2
3737
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-09 11:36 AM

Hello Tien Dat

"Control Board Initialization Progress…” means, it is try to reboot by itself , this kind of symptoms are observed when the unit in Turned on with the input supply, but important thing is it get disappears after sometime, so what i want to understand is, did this symptom was continuously displaying on the screen.

If the answer is Yes, then it is due to some event happened in the unit.

From the image shared, i could see Red Flag was pop-up in the HMI, it clearly determines that there could be some event in the unit.

Can you capture the fault event by pressing the Red flag,  i mean when you press the Red flag, it will take you to the next screen , where you can see the fault event . Please capture a small video or an similar kind of image and share it with us.

In addition, i recommend to download the Event log file from the HMI .

Event Log screen displays events that occurred.

Touch an event to select it.

Press the magnifying glass icon  to display the details for that event.

You can save the Event Log to a USB storage device.

Once it is connected, press this icon to save the file.

In addition to that, please collect the commercial reference , unit serial number and is the unit is standalone or connected in parallel.

Note: After collecting all the detail, i recommend you to raise a BFO case through your country "CCC" team, Customer Care Center. Here below attached the link in both English and Vietnamese

English

https://www.se.com/vn/en/work/support/customer-care/contact-schneider-electric.jsp

 

Vietnamese

https://www.se.com/vn/vi/work/support/customer-care/contact-schneider-electric.jsp

 

Regards

Arunprasad
Reply
tien_dat
tien_dat Explorer
Explorer

Posted: ‎2023-05-09 05:09 PM

0 Likes
1
3732
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-09 05:09 PM

Thanks, Arunprasad,

I send the nameplate of the product, event log, T&C file as an attached file. 

The active harmonic filter appears in this message only with unit status 1/4. After appearing this message, then PCS+ could not permit it to run.

We will send you a video about red flags as you guide later

Notes, the unis operates  in standalone mode

 

 

 

Attachments
AL230430000000-T&C.txt
AL230508010000-Evenlog.txt
Reply
Arunprasad
Arunprasad Mentor
Mentor

Posted: ‎2023-05-10 12:05 AM

0 Likes
0
3719
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-10 12:05 AM

Hello Tien ,

As i mentioned above,

Press the Red flag and capture the Event that display in the HMI. 

Please raise a BFO Case in CCC, we don't use this forum to discuss  more in detail.

So again i request you to raise a case and add the details to the BFO Case.

Hope you can understand.

Regards

Arunprasad
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore