Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Link copied. Please paste this link to share this article on your social media post.
We are using Varlogic NRC12 model with MCU converter for the Modbus communication. Setting of Parity is EVEN it is fixed and we can’t change.
SCADA (Seimens) supplier required Parity is NONE. can you please advice the solution.
Link copied. Please paste this link to share this article on your social media post.
Hi Basim, hope you are doing well.
Unfortunately there is no way to have parity NONE or ODD at the NRC12. Now with the new VarPlus Logic this option is available. This is the answer of our Expert Support in France for the same question in a bfo case.
Cheers!!
Neide - TSC SouthAmerica
Link copied. Please paste this link to share this article on your social media post.
Hi Basim, hope you are doing well.
Unfortunately there is no way to have parity NONE or ODD at the NRC12. Now with the new VarPlus Logic this option is available. This is the answer of our Expert Support in France for the same question in a bfo case.
Cheers!!
Neide - TSC SouthAmerica
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.