Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Link copied. Please paste this link to share this article on your social media post.
We are using Varlogic NRC12 model with MCU converter for the Modbus communication. Setting of Parity is EVEN it is fixed and we can’t change.
SCADA (Seimens) supplier required Parity is NONE. can you please advice the solution.
Link copied. Please paste this link to share this article on your social media post.
Hi Basim, hope you are doing well.
Unfortunately there is no way to have parity NONE or ODD at the NRC12. Now with the new VarPlus Logic this option is available. This is the answer of our Expert Support in France for the same question in a bfo case.
Cheers!!
Neide - TSC SouthAmerica
Link copied. Please paste this link to share this article on your social media post.
Hi Basim, hope you are doing well.
Unfortunately there is no way to have parity NONE or ODD at the NRC12. Now with the new VarPlus Logic this option is available. This is the answer of our Expert Support in France for the same question in a bfo case.
Cheers!!
Neide - TSC SouthAmerica