New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
NRC12 Parity
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2016-08-2108:25 AM
NRC12 Parity
We are using Varlogic NRC12 model with MCU converter for the Modbus communication. Setting of Parity is EVEN it is fixed and we can’t change. SCADA (Seimens) supplier required Parity is NONE. can you please advice the solution.
Link copied. Please paste this link to share this article on your social media post.
2016-09-0210:43 AM
Hi Basim, hope you are doing well.
Unfortunately there is no way to have parity NONE or ODD at the NRC12. Now with the new VarPlus Logic this option is available. This is the answer of our Expert Support in France for the same question in a bfo case.