Meter 1 Pulse per 1 kWh
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2016-07-0509:15 AM
Hi Sven,
Yes, this should be possible. If you look at the section for the particular meter model in the Device Configuration section of the user manual, you can see the path to the setup screen and the values available listed under Pulse Constant.
For example, the iEM3100 info is listed under "Configuration menu for iEM3100 / iEM3110 / iEM3115 / iEM3300 / iEM3310", and the pulse constants available are 100, 200, 1000, 1, 10, 20.