MODBUS exeption response from slave device ION9000

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
huseyinb
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
12
1004

MODBUS exeption response from slave device ION9000

Hi,

 

When i can write data to register with modscan i get this error,

 

how can i solved this problem

 

image.png

Hüseyin Bayram

Accepted Solutions
Charles_Murison
Picard Picard
Picard
0 Likes
0
976

Re: MODBUS exeption response from slave device ION9000

Hello Hüseyin,

 

Currently the ION9000 does not support reading data recorder values via modbus. The document has this ranged reserved for possible future use.

 

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

12 Replies 12
Charles_Murison
Picard Picard
Picard
0 Likes
11
997

Re: MODBUS exeption response from slave device ION9000

Hello Hüseyin,

 

Would need to know a lot more information.

What registers are you trying to write to?

What values are you try to write? 

Modbus Gateway enabled?

What device ID does the request go to? 

Do you know what exception you are getting back?

 

I assume you are talking to an ION9000 and not a device downstream of it.

L4 Prime for Advanced metering and Utilities
huseyinb
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
10
991

Re: MODBUS exeption response from slave device ION9000

Hi Charles,

 

I tried Data Recorder with 53001 register address,

 

Hüseyin Bayram
Charles_Murison
Picard Picard
Picard
0 Likes
9
988

Re: MODBUS exeption response from slave device ION9000

Most Modbus registers in the ION 9000 are read only. Especially data recorders. what it is that you are trying to do?  

L4 Prime for Advanced metering and Utilities
huseyinb
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
8
983

Re: MODBUS exeption response from slave device ION9000

i need Data Recorder Module values, 

Hüseyin Bayram
Charles_Murison
Picard Picard
Picard
0 Likes
0
977

Re: MODBUS exeption response from slave device ION9000

Hello Hüseyin,

 

Currently the ION9000 does not support reading data recorder values via modbus. The document has this ranged reserved for possible future use.

 

Charles

L4 Prime for Advanced metering and Utilities
Tom_Stevenson
Picard Picard
Picard
0 Likes
6
967

Re: MODBUS exeption response from slave device ION9000

Hi Huseyin

 

Register 53001 is not in the ION9000 register map.  Where are you seeing this information?  Data Recorders are not available through Modbus protocol.

 

Thanks


Tom

Charles_Murison
Picard Picard
Picard
0 Likes
0
964

Re: MODBUS exeption response from slave device ION9000

Hello Tom,

 

This is from ION9000_Modbus_Map_002.000.000.xlsx. I have already highlighted this to product owner.

L4 Prime for Advanced metering and Utilities
huseyinb
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
1
960

Re: MODBUS exeption response from slave device ION9000

customer need data recorder, they use 3rd party software.

Hüseyin Bayram
Charles_Murison
Picard Picard
Picard

Re: MODBUS exeption response from slave device ION9000

Hello Hüseyin

 

Data recorder information is only supported with ION protocol, not available with Modbus. 

L4 Prime for Advanced metering and Utilities
huseyinb
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
2
954

Re: MODBUS exeption response from slave device ION9000

Hi Tom,

 

I found this register on Register Map,

 

clipboard_image_0.png

Hüseyin Bayram
Yut
Captain
Captain
0 Likes
1
938

Re: MODBUS exeption response from slave device ION9000

Old document "Modbus Protocol and Register Map for ION Devices_70022-0124-01" has described how Modbus Data Recorder retrieval  is. See if it is compatible to the ION9000 but I'm sure the 3rd party software will not be able to retrieve them since in standard Modbus there is nothing  descripe  about data recorder  unless you have to develop custom application.

 

Tom_Stevenson
Picard Picard
Picard

Re: MODBUS exeption response from slave device ION9000

The data recorder bank of Modbus registers are reserved, but are not implemented on the ION9000 as mentioned above.

 

BR

 

Tom