Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

MODBUS exeption response from slave device ION9000

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • MODBUS exeption response from slave device ION9000
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
570
Mehran_Mehrnia
Mehran_Mehrnia Champion
201
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
huseyinb
huseyinb Mentor
Mentor

Posted: ‎2019-08-09 12:23 AM

0 Likes
12
4485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-09 12:23 AM

MODBUS exeption response from slave device ION9000

Hi,

 

When i can write data to register with modscan i get this error,

 

how can i solved this problem

 

image.png

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2019-08-21 04:19 PM

0 Likes
0
4456
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-21 04:19 PM

Hello Hüseyin,

 

Currently the ION9000 does not support reading data recorder values via modbus. The document has this ranged reserved for possible future use.

 

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 12
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2019-08-09 09:08 AM

0 Likes
11
4477
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-09 09:08 AM

Hello Hüseyin,

 

Would need to know a lot more information.

What registers are you trying to write to?

What values are you try to write? 

Modbus Gateway enabled?

What device ID does the request go to? 

Do you know what exception you are getting back?

 

I assume you are talking to an ION9000 and not a device downstream of it.

L4 Prime for Advanced metering and Utilities
Reply
huseyinb
huseyinb Mentor
Mentor

Posted: ‎2019-08-19 02:07 AM

0 Likes
10
4471
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-19 02:07 AM

Hi Charles,

 

I tried Data Recorder with 53001 register address,

 

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2019-08-19 09:34 AM

0 Likes
9
4468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-19 09:34 AM

Most Modbus registers in the ION 9000 are read only. Especially data recorders. what it is that you are trying to do?  

L4 Prime for Advanced metering and Utilities
Reply
huseyinb
huseyinb Mentor
Mentor

Posted: ‎2019-08-19 11:12 PM

0 Likes
8
4463
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-19 11:12 PM

i need Data Recorder Module values, 

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2019-08-21 04:19 PM

0 Likes
0
4457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-21 04:19 PM

Hello Hüseyin,

 

Currently the ION9000 does not support reading data recorder values via modbus. The document has this ranged reserved for possible future use.

 

Charles

L4 Prime for Advanced metering and Utilities
Reply
Tom_Stevenson
Tom_Stevenson Champion
Champion

Posted: ‎2019-09-05 09:42 AM

0 Likes
6
4447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-09-05 09:42 AM

Hi Huseyin

 

Register 53001 is not in the ION9000 register map.  Where are you seeing this information?  Data Recorders are not available through Modbus protocol.

 

Thanks


Tom

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2019-09-05 10:48 AM

0 Likes
0
4444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-09-05 10:48 AM

Hello Tom,

 

This is from ION9000_Modbus_Map_002.000.000.xlsx. I have already highlighted this to product owner.

L4 Prime for Advanced metering and Utilities
Reply
huseyinb
huseyinb Mentor
Mentor

Posted: ‎2019-09-06 01:46 AM

0 Likes
1
4440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-09-06 01:46 AM

customer need data recorder, they use 3rd party software.

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2019-09-06 02:34 PM

1 Like
0
4437
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-09-06 02:34 PM

Hello Hüseyin

 

Data recorder information is only supported with ION protocol, not available with Modbus. 

L4 Prime for Advanced metering and Utilities
Reply
huseyinb
huseyinb Mentor
Mentor

Posted: ‎2019-09-09 06:45 AM

0 Likes
2
4434
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-09-09 06:45 AM

Hi Tom,

 

I found this register on Register Map,

 

clipboard_image_0.png

Reply
Yut
Yut
Leader

Posted: ‎2019-10-11 01:13 AM

0 Likes
1
4418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-10-11 01:13 AM

Old document "Modbus Protocol and Register Map for ION Devices_70022-0124-01" has described how Modbus Data Recorder retrieval  is. See if it is compatible to the ION9000 but I'm sure the 3rd party software will not be able to retrieve them since in standard Modbus there is nothing  descripe  about data recorder  unless you have to develop custom application.

 

Reply
Tom_Stevenson
Tom_Stevenson Champion
Champion

Posted: ‎2019-10-11 11:44 AM . Last Modified: ‎2019-10-11 11:45 AM

2 Likes
0
4411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-10-11 11:44 AM

The data recorder bank of Modbus registers are reserved, but are not implemented on the ION9000 as mentioned above.

 

BR

 

Tom

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore