Hello,
You can use the terminals 21 and 23 to monitor the ON/OFF signal (Dry contact) from circuit breaker for DI1.
The 22 (0V) and 23 (+24V) terminals can be used if the input signal is potential signal (24VDC) for DI1.
Regards,
Ramasamy N