Hello Community,
"You need to be able to configure the digital output per pulse, specifically it requires that the pulse be at least 100 milliseconds but defaults to 20 milliseconds.
The query is what would be the way, if it exists, to configure this parameter in the meter? Since reviewing the manual it only indicates how to do it but by the ION SETUP. Now, another question would be what I need to configure this equipment through the ION SETUP since they have Modbus communication via RS485, so it is complicated to connect through the PC, would we need a converter?"
Please, thanks!
BR
Link copied. Please paste this link to share this article on your social media post.
Hello @Christian_Sáenz ,
PM2130 digital output pulse ON time (20, 25, 50, 100mS) can be configured by user in ION setup from the firmware version v1.4.0 onwards,
You can refer the "ION setup device configuration guide" for more details about the connecting the meter and configure in ION setup.
https://www.se.com/th/en/download/document/7EN02-0293/
Regards,
Ramasamy N
Link copied. Please paste this link to share this article on your social media post.
Hello @Ramasamy_N ,
Do you know if possible to change the digital output pulse width for PM2130?
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @Christian_Sáenz ,
PM2130 digital output pulse ON time (20, 25, 50, 100mS) can be configured by user in ION setup from the firmware version v1.4.0 onwards,
You can refer the "ION setup device configuration guide" for more details about the connecting the meter and configure in ION setup.
https://www.se.com/th/en/download/document/7EN02-0293/
Regards,
Ramasamy N