Is there a list of approved CT's and VTs for use with ION8800 meter ? My customer's application will range from LV up to 232kV

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Re: Is there a list of approved CT's and VTs for use with ION8800 meter ? My customer's application will range from LV up to ...
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
495
Ramasamy_N
Captain Ramasamy_N Captain
115
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
95
Robert_Lee
Admiral Robert_Lee Admiral
92
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
sesa208484_brid
Crewman sesa208484_brid Crewman
Crewman

Posted: ‎2015-10-15 03:43 AM

0 Likes
3
1205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-10-15 03:43 AM

Is there a list of approved CT's and VTs for use with ION8800 meter ? My customer's application will range from LV up to 232kV

My customer is considering using ION8800 rack mounted meters with their mobile generator sets in a modular substation environment.

Does Schneider have experience with/access to a list of approved CT's and VT's ranging from LV up to 232kV ?

Tags (1)
  • Tags:
  • ion8800
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Yut
Captain Yut
Captain

Posted: ‎2015-11-15 07:48 PM

0 Likes
0
1139
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-11-15 07:48 PM

Any accepted CT and VT from project owner would be OK. We have installed hundred of ION8000s  here with many brand of VTs and CTs mostly ranging from  69kV to 500kV.

Reply
sesa189395
sesa189395 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2015-12-17 05:18 AM

0 Likes
0
1139
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-12-17 05:18 AM

Hi Alan,

Did you receive any further responses elsewhere to resolve this question?

Patrick Wilkerson

Sanjeet Sahota

Reply
sesa50168
sesa50168 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2015-12-17 08:45 AM

1 Like
0
1139
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-12-17 08:45 AM

Hi Alan -

From the meter manufacturing perspective, we don't have a list of preferred CT & PT manufacturers, except of course in the LV range, where we have our own range of CTs.  When using a high end meter, such as an ION7650 or 8800, generally the customer or consulting engineer will specify the CTs and PTs.  Our primary recommendation is to use metering class devices.

Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of